Thread: Line set sizing?

  1. #1
    Join Date
    Jun 2008
    Location
    Southern,N.J
    Posts
    1
    Post Likes

    Line set sizing?

    What affects or damage can occur when running smaller diameter lines for a discharge or suction line? I know deff higher head pressures. I'm new to the field experts please chime in..Also new to the site hello everyone..

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Lower capacity
    Lower efficiency
    Possible shortened compressor life.

    Welcome

  3. #3
    Join Date
    Sep 2003
    Posts
    139
    Post Likes
    If the suction line is too small, you may not get proper oil return to the compressor. You also can have a reduced capacity.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    An undersize vapor line doesn't hurt oil return.
    Too large of a vapor line can.

  5. #5
    Join Date
    Sep 2003
    Posts
    139
    Post Likes
    WOW! I hope you don't do refrigeration! OOPS... Read it wrong Beenthere! Need to assure proper velocity Horizontal increase size, vertical decrease.
    Last edited by heatingairman; 07-06-2008 at 10:12 PM. Reason: Read wrong

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Both A/C and refrigeration.
    A vapor line 1 size undr will never hurt oil return.
    The next size up however can on installs with the condenser vertically above.

    Recommended min suction line velocity is 1000 FPM. I have vapor line sizing charts for unit that allow the vapor line to be sized for up to 3000 FPM.

    I don't have any that approve less then 800 FPM. And they don't want a vertical rise to the condenser.

    If you have line set sizing charts that allow 500FPM velocity in the vapor line, post them.

  7. #7
    Join Date
    Sep 2003
    Posts
    139
    Post Likes
    I don't think anyone will go out on a limb with 500fpm

  8. #8
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    So is it safe to say it's a trade off of capacity for smaller sizes and velocity is not so much a concern or oil return......and the LL is way more important to capacity?

    Also how important are traps in vertical rises of 50+ ft? I might be subjecting myself to these before to long. Not sure if they even put traps in @ the recommended heights.....for oil return?

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Involved topic Jon.

    Within reason, you can compensate a little for a slightly smalled liquid line, more then a vapor line.

    Did you get that email I sent you. It has some line set sizing info in it.

  10. #10
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    I'll check....I didn't think this was the right forum to get to involved.


    was that just now or recently in the past?

  11. #11
    Join Date
    Sep 2003
    Posts
    139
    Post Likes
    I sent yo an email too bigjon.

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Within teh last few days..
    I don't remmember which.

  13. #13
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    i'll go back over I'm sure i got it.

  14. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Just checked. I sent it on the 4th.

  15. #15
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    Quote Originally Posted by beenthere View Post
    Just checked. I sent it on the 4th.
    Sorry not trying to be annoying.....Do you remember the name of the file...maybe I put it in my storage and mean to go back and go over it and forgot. I don't doubt I would have saved it....been about a case of beer thrown in theirbecause of the whole fourth (looks around with a kinda guilty look)


    Thanks heatingairman for the Lennox line set guidelines.

  16. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    LMAO.

    You won't believe the topic.

    Its called.
    Line set sizing.

  17. #17
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    Okay I found it sorry

  18. #18
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Goes into pressure drop/increase for vertical lines.
    Not too deep.
    Also piston size increase/decrease for excess vertical heigth.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •