Quote Originally Posted by JJMJD View Post
I will post when I get the info from the contractor. Current bid just says (a) XC-15-036 3 ton 15 SEER A/C, G61MPV-90 90,000 BTU 94% efficent gas furnace with variable speed blower and CX-33-038 3-ton coil and (b) XC-15-030 2-1/2 ton 15 SEER A/C, G60UHV-070 70,000 BTU 80% efficent gas furnace with variable speed blower and CX-33-038 3-ton coil. The upstairs unit is in a closet and is horizontal (up-flow). Thank you.

I do not see a C33-38 or a CX34-38 for a 90K btuh furnace match, only 70K, so there must be a mistake.

There is no CX33, it's C33 or CX34 so you need to clarify.

ARI 3007821 gives you 15.50 SEER with a G60UHV-36B-070, a C33-38 with a TXV and a XC15, so that one works.

ARI 3007978 is the same using a CX34 so that's a match.

You also need to clarify weather horizontal or upflow, you said it's both and in a closet, so I suspect upflow!