    Pipe in a 1/4" N. O. solenoid valve

    Connecting discharge to suction. Power the solenoid coil parallel with the coil of the compressor contactor but through a two second time delay relay.

    That would give you full unloaded compressor start up.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  2. #15
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,775
    And if the timer goes out, it gives you a good reason to get a new system.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #16
    Join Date
    Sep 2002
    Posts
    13,549

    Make the bypass line a big loop

    And put a thermostat on it near the suction connection. If it gets over the set-point it could either trip an alarm circuit to your alarm company or shut the unit down.

    Don't be silly - we're saving the compressor here!



    Quote Originally Posted by beenthere View Post
    And if the timer goes out, it gives you a good reason to get a new system.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  4. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,775
    Quote Originally Posted by Poodle Head Mikey View Post
    And put a thermostat on it near the suction connection. If it gets over the set-point it could either trip an alarm circuit to your alarm company or shut the unit down.

    Don't be silly - we're saving the compressor here!
    LOL..
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event