    Alerton Visual Logic Question

    Does anyone have and can send me PDF's on Visual Logic programming and possibly a Users Manual?
    I've got a job that has a BV (Binary Variable?) that's sent to all the parallel fan VAV box controllers. It is turning on all the fans even though the boxes are at 100% cooling demand. This is mixing the primary air (55*) with the heating air (return air) and providing 65* air causing the zones to overheat. (At least it's not turning on the electric heat also)
    Someone obviously got confused between series and parallel boxes.
    I see in the Visual Logic VAV file where the BV "input" is, but do not know how to find where it comes from, or change it and the program.
    If I remove the BV from the fan input of the VAV controllers, would it revert to proper canned fan operation?
    Sorry, I do not have any version or model numbers yet.
    TIA
    jogas
    Last edited by jogas; 07-06-2008 at 11:08 AM.

  2. #2
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    910
    Hi jogas,
    It should be in your inbox. Let me know if you didn't get it. I'm having some email issues.

  3. #3
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,720
    Quote Originally Posted by The Reaper View Post
    Hi jogas,
    It should be in your inbox. Let me know if you didn't get it. I'm having some email issues.
    Got it.
    Thank you very much.
    jogas