    indirect water heater

    Does the addition of a 40 gal indirect water heater with priority require a larger boiler, if existing 100000 btu hydronic/baseboard system comfortably heats house on coldest days.

  2. #2
    Join Date
    Sep 2006
    Location
    Leavenworth KS
    Posts
    308

    indirect

    Most likely No. Need more details.
    Mike

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,875
    Very doubtful you would need a bigger boiler.

    Unless you intend to take hour long hot showers.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Jul 2001
    Location
    Gold Coast of Connecticut
    Posts
    4,578
    I have a 100K Net boiler with 3 zones and a 4th zone for my 40 gallon indirect. We take 2 showers at once, then 2 back to back. Never a shortage and the home temp stays pretty constant. A big tub will whipe it out, and if you have issues with running out you can install a priority to keep the heat off as long as it is making hot water.