Long lineset concerns?
My installer is planning to place the AC condenser (Goodman SSX160601) on a concrete pad behind the house. To connect it to the coil in the attic, the lineset would require a 30 ft rise, and then about 40 ft across the attic.
I wondered about the 70 ft length of the lineset, and he said that as an alternate, he can put the condenser on the garage roof, which would result in a 12 ft rise and 10 ft in the attic. But this would require building a support structure on the roof, which he seems reluctant to do. It would also be very visible from the backyard, which I don't like too much.
Should I be concerned with the long lineset and go for roof mounting, or should I go with the original plan? Are there any special steps he needs to take for the long lineset (he mentioned using 1 1/8" line, a hard start capacitor, and crankcase heater)?
Thanks,
Mark
-
07-04-2008, 01:59 PM #2
with a run like that i would also recomend a pump down selenoid sized for the tonage and type refrigerant at the evap coil
-
07-04-2008, 02:10 PM #3
Regular Guest
- Join Date
- Oct 2005
- Posts
- 165
And you would go with the long lineset run over the roof mounting?
-
07-04-2008, 03:15 PM #4
Your contractor needs to check on the refrigerant line sizing chart, I don't think the two stage scroll can handle a verticle lift of more than 20-feet. I haven't had to deal with this in a long time and don't have access to literature right now.
I do agree with the CCH, not so much on the start assist as long as the system has a timer. The LL solenoid is a very good idea I would even put the solenoid on a 10 or 15 second delay.
-
07-04-2008, 03:25 PM #5
-
07-04-2008, 03:28 PM #6
Maybe, a CCH.
No real reason for a LLSV.
He should check with Goodman to see what they say about teh line set length, and what should or shouldn't be done in the way of adding or not adding componets.
After all, they are the ones that can void warranty.
-
07-04-2008, 03:35 PM #7
Professional Member
- Join Date
- Apr 2007
- Posts
- 6,286
Long line set recommendations from Goodman don't start suggesting accessories until 80 ft.
Is it R-410A or R-22?
-
07-04-2008, 03:37 PM #8
-
07-04-2008, 03:42 PM #9
-
07-04-2008, 03:57 PM #10
Regular Guest
- Join Date
- Oct 2005
- Posts
- 165
It's a R-410 system. From what I can find on Goodman's website, the instructions for this condenser say:
"These sizes are suitable for line lengths of 74 feet or less. If a
run of more than fifty feet is required, refer to Remote Cooling
Service Manual, or TP-106 Long Line Set Application R-22, or
TP-107 Long Line Set Application R-410A or contact your distributor
for assistance."
When I look in the TP-107, it recommends the accessories (hard start, CCH) only for > 80 ft. It doesn't say anything about elevation other than the max elevation is 25 ft if condenser is above coil, but mine is the reverse. I didn't find any restrictions on condenser being below coil.
Regardless, it sounds like there are ways to make it work (maybe with some accessories), which I would prefer over the roof mount idea. I just want to make sure that we won't get in trouble with the long lineset.
-
07-04-2008, 04:09 PM #11
thanks been and classical for explaining
from what i remember from school years ago on a high lift you should run a certain length horizontal for every certain foot vertical
-