    Longer Lineset Needs Larger Size?

    Old unit is still running, but it's got to be on its way out (20+ years old). It will probably be replaced with a 410 refrigerant unit, and so my question is: With a lineset run of 40 feet, with 8 feet of that being a vertical run (the unit is in the attic), will it need a larger-diameter-than-usual lineset? If so, I guess that solves the question of clean vs. replace on the lineset...

  2. #2
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    4,744
    Post Likes
    It depends on what size lineset you have now as well as what size unit you will be putting in. It might not even have the right size to run the 410 to start with.

  3. #3
    Join Date
    Sep 2006
    Location
    Leavenworth KS
    Posts
    311
    Post Likes

    Cool line set

    Not knowing your current line size. Tends to limit your answer and most likely provide with you bad information. Prior to changing your Climate control system. You should have these things done. A load calculation(manual J ), Review of existing duct system(check for correct sizing and leak tightness), check the duct insulation system for proper type thickness along with sealing issues. Your contractor should preform all of these before submitting a proposal. You may or may not see these things. The contractor may charge you to see these some times.The firm I work for does if the customer wants the information before committing to do the work. The proposal stage(quote, estimate) should involve a complete look at your home and they should ask some questions.They may even recommend filtration system adjustment.

    If I am not mistaken your local area the duct system is in the attic. You may be looking at a smaller system if improvements to the home have been made since the last calculations where done. If somebody even did preform a calculation. Increasing the size is not wise without more information


    Mike
    Mike

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    40' isn't a long line set.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •