    Another AC won't cool below 80F Problem

    I live in AZ and one of my Goodman 3.5 ton SEER 12 units (only 2-year-old) is having trouble cooling the rooms below 80F in daytime after running for at least 3 hours straight (outside temp 100 to 110F). Using a laser thermometer, the temp coming out of the vents varies from 64F to 69F. My attic has R30 insulation. I've just changed the filter, and cleaned the condenser coils outside my house.

    When the tech came, here are some measurements he took:

    Sub cool: 11F / 10F
    Superheat: 5F / 5F
    Low side PSI: 75 / 77
    High Side PSI: 280 / 260
    Compressor: 22.1 - 18.3
    Condenser: 1.6 -1.1

    He told me those numbers look fine, and all he did is changing the piston from size 74 to 78 (according to him this will increase freon flow), and 'flush' the system.

    Anyway, those didn't help at all, and now I have to call them back and do more diagnostics. What else can I ask them to look into (besides duct leaks)?

  2. #2
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    A load calculation....that system might not be big enough to handle what you want it to do. 80 degree indoor with 110 outdoor is a large difference.
    If everything was always done "by the book"....the book would never change.

  3. #3
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,022
    Post Likes
    Did the system ever cool better than it does right now?

    Measure the temperature drop accross the air handler; if it's significantly greater than what you're getting at the vents, you could have a leaky return air duct or sections without (duct) insulation.

  4. #4
    Join Date
    Jul 2008
    Location
    Southern California
    Posts
    142
    Post Likes
    If your room temp is 80 (return air) and the supply air temp is 69 that is only an 11 degree TD, if the unit was operating normally it would be closer to 20 degrees. Its time for somebody else to look at it.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,516
    Post Likes
    Hope he still has the old piston.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Post Likes
    Superheat of 5
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,516
    Post Likes
    happens with dirty ID coils.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Oct 2005
    Location
    phoenix az
    Posts
    429
    Post Likes
    Hmmm! I flush a toilet or flush a radiator but changing a piston to flush an A/C
    "Do not let what you can't do interfere with what you can do"

    "Do what you can do the best that it can be done and no one will ever know what you can't do"

  9. #9
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    Quote Originally Posted by skorepeo View Post
    Hmmm! I flush a toilet or flush a radiator but changing a piston to flush an A/C

    yea didnt you know it all goes down hill from there

  10. #10
    Join Date
    Jul 2008
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by skorepeo View Post
    Hmmm! I flush a toilet or flush a radiator but changing a piston to flush an A/C
    Sorry, perhaps I shouldn't use the word 'flush'. According to the work detail, it's a 'System Evac', which he told me if something is blocking the line, doing that might help 'unblock' it.

    I went outside and check on my condenser unit, I see water droplets forming on the cold line running into the condenser unit, is this normal?

  11. #11
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Post Likes
    Quote Originally Posted by johndoe74 View Post
    Sorry, perhaps I shouldn't use the word 'flush'. According to the work detail, it's a 'System Evac', which he told me if something is blocking the line, doing that might help 'unblock' it.

    I went outside and check on my condenser unit, I see water droplets forming on the cold line running into the condenser unit, is this normal?
    Condensation is normal but you still need to have the system serviced and diagnosed properly.

    Believe us when we say cheap is not the route to take when it comes to HVAC.
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  12. #12
    Join Date
    Oct 2005
    Location
    phoenix az
    Posts
    429
    Post Likes
    You need a good tech now quit with this guy and get a more experienced tech while your still ahead!!

    I am not trying to bash but from what you say he sounds like a handy man!!
    "Do not let what you can't do interfere with what you can do"

    "Do what you can do the best that it can be done and no one will ever know what you can't do"

  13. #13
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Post Likes

    Thumbs up I agree

    Quote Originally Posted by skorepeo View Post
    You need a good tech now quit with this guy and get a more experienced tech while your still ahead!!

    I am not trying to bash but from what you say he sounds like a handy man!!
    You need to find a real tech before your system dies due to a bad tech.

    It has happened many times before...don't let it happen to you too
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.