    going to ice up

    Im working on a 5ton r22 ac system with a txv, the suction pressure is at 32_33deg saturation, subcooling is at 12°, and superheat at 20°. The indoor temp is around 68°(becaise the customer wants it that cold for their wine). It has an 18"and a 10" return, and 6tons of supply ventilation (haven't checked the static but im assuming that its ok). Is r22 not meant to operate in that low of a load, because when I take the cover off the blower door and suck in warm attic air my saturation goes up to 40°.

  2. #2
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    Restricted return, or low supply air flow???

    52 degree suction line, it isn't freezing due to a refrigerant issue.
    "If history repeats itself I am so getting a dinosaur"

  3. #3
    Join Date
    Mar 2015
    Posts
    62
    Post Likes
    Thread Starter
    Return looks good, I took the covers and filters off and it changed nothing.

  4. #4
    Join Date
    Mar 2015
    Posts
    62
    Post Likes
    Thread Starter
    Supposedly it has worked fine for years

  5. #5
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    I think that is normal ,considering you are on the verge of refrigeration. The lo side load is low so the suction should also be lower. Does the evap freeze over?

  6. #6
    Join Date
    Mar 2015
    Posts
    62
    Post Likes
    Thread Starter
    Hasnt yet but with the saturation bordering freezing im afraid it will. Im almost tempted to open expansion valve a hair to bring it up a little

  7. #7
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Check the existing SH , leave it at normal.They might be lucky enough to have enough "off cycle defrost" just like refrigeration.

  8. #8
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Why were you called out? It probably has run like that all the time, since what they are doing is basically a refer unit.
    UA Local 32 retired as of Jan 2020

  9. #9
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    How much wine do they have? sure seems like a waste of a 5 ton unit

  10. #10
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Drink enough Ripple Wine and you will see a waste

  11. #11
    Join Date
    Mar 2015
    Posts
    62
    Post Likes
    Thread Starter
    I was called out due to a compressor burnout, replaced compressor flushed lines and noticed system has no filter dryer and no screen before piston. Afyer replacement turned sysyem on and my suction was way low, about 45_50 psi and icing up. Cleaned cpndenser coil and debri of condenser fan motor. Ran again, and could not get my suction psi up, or superheat down. So I suspected a plugged cap tube, so we replaced coil. Now my superheat is better and suction stauration is better but still not were I would like it.

  12. #12
    Join Date
    Oct 2007
    Location
    Broward County, FL.
    Posts
    675
    Post Likes
    Check for a dryer inside the cond. unit. It may be plugged.
    I miss you mom and dad.

  13. #13
    Join Date
    Mar 2015
    Location
    ARK.
    Posts
    3,389
    Post Likes
    OK. Your Entering the Freeze Up Zone. (tv pun intended)

    You have TXV trouble.
    When you enter the Zone,you must rethink your Basic's.
    You HAVE to Increase your SH,Starve the Evap,lower Charge(in our case),Adjust CFM.
    We did this on an Old RUUD Gaspac with Captube's.NO piston or TXV.
    I would go after the TXV and if it was adjustable,Check to see if it's been molested..
    Not sure how far I can go Here at times so I'll leave you with this adv.
    No matter how long you have been doing this,
    Go back and reread the Basic's.You WILL Learn something.
    Why is it called,an Act of GOD when IT has Nothing to do with Him?
    Will of the Devil would be more appropriate IMO.Just Saying.
    PSALMS, 18 & 25.
    I am Tired of High Efficiency Propaganda.

  14. #14
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes
    OAT? Indoor wet bulb? Temperature drop?

    Yeah, I know, this is a TXV, but low load/low temperature is going to bring low suction pressure under certain circumstances. This is medium refrigeration after all.

  15. #15
    Join Date
    Mar 2015
    Posts
    62
    Post Likes
    Thread Starter
    Oat was 75, wet bulb65, did not get temp drop across coil, but differential is 18

  16. #16
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes
    Quote Originally Posted by claysontech View Post
    Oat was 75, wet bulb65, did not get temp drop across coil, but differential is 18
    When you mean differential, are you talking about the difference between return and supply temperature? If so, that would be your temperature drop.

    Assuming airflow is perfect at both the condenser and evaporator, I would say low load is the problem. 68 degree return is very low and if there isn't a lot of moisture in the air, that can cause your low side saturation temperature to drop below freezing. This doesn't necessarily mean the coil will freeze over because if there's a lack of moisture in the air, there's nothing to freeze on the coil. You might see some light frosting, but it's perfectly normal considering the conditions.

    My only other thoughts are you might still be low by 1/2 a pound or so. Some systems operate with subcooling as high as 14 degrees, so 12 degrees isn't high by any stretch. Once you start getting above 15 degrees, then you may have an issue.

    Keep in mind residential systems aren't in controlled environments, so it's useless to split hairs in some cases.

  17. #17
    Join Date
    Mar 2015
    Posts
    62
    Post Likes
    Thread Starter
    I really appreciate all the feedback.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •