    It's all about proper Installation !

    Long time reading here (learning) mostly - question time now.

    A "consistent" theme here, without regard to system manfufacturer, or even sizing to a degree is It's all about a proper installation. With literally thousands of contractors in any major large metropolitan area, they all pitch the same line.

    The question is, how is one to know what is a "good install" as opposed to an "ok" or "really crappy" install? After 11 years in our house with the existing A/C (2.5 ton Carrier) during summers I've never been to get the house comfortable....the A/C ran continuously from 10 AM till 2 AM before it clicked off. And, this was for the downstairs unit! Not even discussing the upstairs yet! You can only imagine the utility bills.

    So, having had 4 bids out of hundreds in my area, one actually did a computer version of the Manual J Load Calculation and it came up to minimum 3.5 ton for the downstairs (2900 sq ft / 1700 down- 1200 up)

    After quickly learning the 1/2 ton units dont come in newer technology dual speed compressor / fans, went with a 4 ton Amana ASX16 seer entire sytem. Amazing now to be able to hold 68 degrees even on the hottest days 95+. System cycles high for a couple of minutes then to low speed for 15 min or so then as needed back to high speed again or off late in the day and at night.

    Sorry...back to the question. Anyway...... The contractor I choose came in with the LOWEST bid, and I offered the other 3 bidders a chance to meet or beat their price - matching component to component / apples to apples comparisons- NONE of them ever called back again!!!

    So.. they came out 2 days later and installed a complete new system (incl gas furnace). BBB showed in biz 22 years, 3 complaints, all resolved in last 36 months, all the certifications and members of various HVAC groups, etc, etc. - They were not some fly-by-night operation!.

    As a DIY sort of guy, I feel fairly knowledged in a lot of things, especially common sense applictions. The guys did what I consider to be a nice install. Added another supply vent and a 12 x 12 return air in another location to improve circulation and add more return capacity (CFM's).

    OK.. SO.. How do I actually KNOW, what is a good install and what isn't?

  2. #2
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    it is the way you want it

    it works the way you were told it would

    you are happy with the work and the additudes of the porple there and the quality or thier all arround ethics

    these are what count IMO

  3. #3
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    You got a good installation if you can't find a thing about it that makes you question it's quality. Every room and space that is conditioned stays at an even temperature and can be heated or cooled as you'd like it. You installed equipment matches the quote as far as model numbers and size. When they were done wherever they worked was as clean or cleaner than when they got there. Everything about the system, it's operation and maintenance was described to you in detail. The start up was documented on each part of the system. They took down readings and measurements for future reference during routine maintanance to insure everything is within manufactures specs.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  4. #4
    Join Date
    Jan 2008
    Location
    California
    Posts
    110
    Post Likes
    Good installs meet current code and comply with manufacturer recommendations and guidelines. They have correct clearances and observe best construction installation practices, incorporating trade knowledge to ensure safe, efficient operation and provide the full expected lifespan of service to new owner.

    A great install reflects signature quality work, pride in tradecraft and a sense of 'we touched it - we own it'.

  5. #5
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Post some pictures and they'll let you know...

  6. #6
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Pictures and insist on a static pressure test.

    Doesn't sound like enough duct work was added for what sounds like an additional ton of A/C.
    Last edited by dash; 06-28-2008 at 10:47 PM.

  7. #7
    Join Date
    Aug 2003
    Posts
    227
    Post Likes
    Sounds like You did your "home work" and Shopped around – got what you payed for (and did not skimp on Eq,) That help allot - also you offered others a chance to match or beat your lowest bid!

    Sounds like it's meeting your expectations (cold and better air flow though-out house) and from your point of view - they did a good job

    I would offer them to come check system out after 6 mo and 1 yr - to check performance! (even if you pay service fee - maybe they will give you a discount because your a Happy customer) so while its under warranty! may catch anything while it is.

    To me sounds good - especially hearing so many "NIGHTMARE" Stories on here!

  8. #8
    Join Date
    Jun 2008
    Location
    DFW area
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by dash View Post
    Pictures and insist on a static pressure test.

    Doesn't sound like enough duct work was added for what sounds like an additional ton of A/C.
    Here are some pics........ (can's seem to make link work to actually show the pics in message.)

    This is the house they are working on - 2800 sq ft. 1600 down 1200 up.

    The downstairs has two large living areas, full kitchen, breakfast room, laundry room, foyer, dining room, full bath, guest bedroom.

    Ducts and returns - 10 toal supply lines - 8 hard insulated pipe and 2 new flex duct (10 in and 8 in)

    Living room 1 & 2 - 16 x 6 supply grill and one 30 x 16 return air (floor level)
    Shared return with Living room 1

    Kitchen, Breakfast area, dining room, guest room, and foyer 12 x 6 supply duct - no returns.

    Laundry room, bathroom 10 x 4 supply - no returns.

    New return, (new shiny flex duct in pics) ceiling mount 14 x 14 - just outside in hall where bath and guest room are.

    New supply (shiny flex duct on top of unit) 12 x 6 in Living Room 1 by outside wall directing air across a major sun heated exterior by day.

    There you have the layout. They wanted to add even more return air, but was all but impossible as upstairs right on top made that impossible.


    Browse thru this link for small picked related pics.

    http://www.c5dreamer.com/hvac/

    For ALL pics - very large, go HERE ---> FOLLOW LINK HERE/
    Last edited by avflyguy; 06-29-2008 at 01:24 AM.

  9. #9
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Here are the rest of the pictures: http://www.c5dreamer.com/hvac/

    Question for the pros:

    I may be wrong, but shouldn't the coil be pointing up from the furnace? http://www.c5dreamer.com/hvac/fullsize/S5001467.JPG

  10. #10
    Join Date
    Apr 2007
    Posts
    626
    Post Likes

    airflow?

    I agree, if it is functioning properly and is up to code, these are the important things. With up-sizing the unit so much, I would question, as it has been mentioned, if the duct-work will support your 4 ton with proper air flow. I have worked on a few of the ASX-16's , good unit in my opinion. I assume you have a new amana AMV variable speed air handler/furnace. Hopefully the dip switches are set to proper cfm, and they have verified second stage operation of your compressor, you cannot hear the difference between 1st and 2nd, and I have found at least 3 with the compressor solenoid plug loose at compressor, straight out of the box. You cannot see this immediately because the compressor has a sound blanket covering it. I rely on amp draw to monitor if second stage has engaged, just because ther is a call for it and your stat is showing 2nd stage, does not gaurantee anything. Not to alarm you, all this may have been checked, just thought I would throw it out there.

  11. #11
    Join Date
    Mar 2008
    Location
    Grundy Co. IL
    Posts
    773
    Post Likes
    Don't see too many Amanas, just tell me the acess panel on the condensor is not on the back, against the house.

  12. #12
    Join Date
    May 2008
    Posts
    17
    Post Likes
    Sounds like you answered your own question. The installation looks good and you are happy with the results.

  13. #13
    Join Date
    Jun 2008
    Location
    DFW area
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by aintitfun View Post
    I agree, if it is functioning properly and is up to code, these are the important things. I assume you have a new amana AMV variable speed air handler/furnace. YES IT DOES Hopefully the dip switches are set to proper cfm, and they have verified second stage operation of your compressor, you cannot hear the difference between 1st and 2nd, and I have found at least 3 with the compressor solenoid plug loose at compressor, straight out of the box. You cannot see this immediately because the compressor has a sound blanket covering it. I rely on amp draw to monitor if second stage has engaged, just because ther is a call for it and your stat is showing 2nd stage, does not gaurantee anything. Not to alarm you, all this may have been checked, just thought I would throw it out there.
    I was at home and observing just about every step. The condensor/compressor came right out of the sealed box, was put onto a new concrete pad. Electrical connections were restored and new line set was installed, purged with Nitrogen and vacuumed prior to running it. I did not see them do anything inside the unit to set or not set the two stage compressor functioning. How would one check the 'compressor solenoid plug' ?

    After a week now with an entirely new system, I am incredibly satisfied with the cooling and how little time it takes now to knock off a couple 2 or 3 degrees.. I mean minutes....the old unit would have taken hours!

    ** They also installed a Honeywell 9000 thermostat. ( I think it is). They had to go through a lot of initial installer programming. I am not confident they were completely comfortable with some of the inputs they made. A few times, the two of them looked like they didn't know for sure. BUT.... it does seem to be running right. How would I check that? They took that programming tutorial with them and only left me with the user manual.

  14. #14
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    They took that programming tutorial with them and only left me with the user manual.
    First, please confirm if it is the VisionPRO 8000 (TH8320/TH8321) or VisionPRO IAQ (YTH9421). Honeywell has the installation instructions/setup info on their website, so you can read it over and look at the settings. I do not recommend that you change any without consulting a professional (or member here) first unless you are sure of what you are doing; you wouldn't want to mess anything up on the new system.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •