    Chiller water and freon temp

    Will the chiller water temperature during the off cycle of a compressor show up as the evaporator temperature of the freon ?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    69,657
    Post Likes
    Not on a pump down system.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Nov 2007
    Location
    Framingham Ma
    Posts
    41
    Post Likes

    water temp showing in freon temp?

    Our system does not pump down it just shuts off the compressor when the thermostat is satisfied.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    69,657
    Post Likes
    Then as long as there is atleast 1 drop of liquid refrigerant in the evap. The water temp will be refrigerant sat temp.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Nov 2007
    Location
    Framingham Ma
    Posts
    41
    Post Likes
    Thank you, Stuart