Results 14 to 26 of 51
Thread: Condensate drain (s)
-
07-01-2008, 08:23 AM #14
Professional Member
- Join Date
- Mar 2005
- Location
- Houston, Texas
- Posts
- 11,644
Ask them how they (or anybody) propose to remove the evap coil in the future. Looks like a poor install. From what I can see in that picture.
-
07-01-2008, 09:27 AM #15
Regular Guest
- Join Date
- Jun 2007
- Location
- North Texas
- Posts
- 20
Mr. Wrangler-
Could you elaborate a little for me? Should there have been some kind of a panel or an access door to get the EC out, what should/could have been done in your opinion?
Thanks
-
07-01-2008, 02:21 PM #16
Professional Member
- Join Date
- Mar 2005
- Location
- Houston, Texas
- Posts
- 11,644
The access panel is there. But,the trapeze (the support for the unit) has what looks like 3/8 all thread rod directly in front of the coil access door. From what I can make out in the picture, you'd have to remove that first,then what would support the unit? Also, the primary drain just doesn't look quite right.
-
07-01-2008, 02:39 PM #17
Regular Guest
- Join Date
- Jun 2007
- Location
- North Texas
- Posts
- 20
The tech came out and drained the pan looking for a leak. He said the area around the TXV where hot meets cold was sweating. He insulated and caulked that and told me to keep an eye on it. Will get pics for anyone interested.
Thanks
-
07-01-2008, 02:44 PM #18
Professional Member
- Join Date
- Mar 2005
- Location
- Houston, Texas
- Posts
- 11,644
I'm not trying to nit pick this install but, you have other issues with this job. It looks a bit on the sloppy side to me.
-
07-01-2008, 02:50 PM #19
Professional Member*
- Join Date
- Aug 2007
- Location
- East central Indiana
- Posts
- 70
That's an EZ Trap. It has a float switch installed and wired to shut the system down in case the drain backs up. The red dial looking thing is a cap that can be removed to use the brush that comes with the setup to clean the pan drain. The outlet is vented by a black plastic tube with an ear for holding the cleaning brush. It's a neat system. The only problem with it is that it won't detect a blockage upstream.
-
07-01-2008, 04:50 PM #20
Professional Member*
- Join Date
- Jan 2001
- Location
- Pamnyra VA.
- Posts
- 699
it looks like crap to me. he should fix it right.why should you be up there looking around. he's the mechanic not you. i'm sure you paid someone good money, let them monitor it.
-
07-01-2008, 07:27 PM #21
Professional Member
- Join Date
- Jan 2007
- Location
- N.E. Ok.
- Posts
- 1,296
-
07-01-2008, 07:45 PM #22
i could be wrong , but it looks like they installed a drain or down spout in the higher outlet of the primary drain and then 90'd it acouple of times so it points straight up. thats pure jake leg. its supposedly for vent , but i don't agree with the need for a vent or an overflow on the higher outlet. maybe if it had another float switch.
"When the people find they can vote themselves money,that will herald the end of the republic" - Benjamin Franklin
"Government is not reason, it is not eloquence, it is force;like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action"- George Washington
-
07-01-2008, 08:01 PM #23
I agree. Was this job done by a company or a one man show. If it was a company have the manager come out to have a look, I bet if the company worth anything he will get you fixed up. Oh yeah tell him you are going to release their name to this site if you dont get answers. If it was a one man show, you get what you pay for, most of the time.
Build it and it will break. Fix it and it will work. Ignore it and will cost more. Patch it and it will get worse. Cross the bridge before the flood.
-
07-01-2008, 08:02 PM #24
-
07-01-2008, 08:12 PM #25
for a dollar you can get a 3/4 pvc cap and end your problem, seriously i only charge a dollar!
"When the people find they can vote themselves money,that will herald the end of the republic" - Benjamin Franklin
"Government is not reason, it is not eloquence, it is force;like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action"- George Washington
-
07-08-2008, 05:38 PM #26
Regular Guest
- Join Date
- Jun 2007
- Location
- North Texas
- Posts
- 20
Problem getting resolved?
After hearing about installation being the most important part of the purchasing decision, I did a lot of looking and interviewing before I selected the company I went with. They were not the cheapest!
However my problems are on-going. The water in the emergency drain pan is coming from the cabinet. The problem lies in several areas. The main drain may not have had the proper slope to operate efficiently. Also, the static pressure was very high, forcing too much return air, causing moisture buildup. The insulation on the inside of the cabinet was wet but not in the plenum.(sp) This is what I observed and have been told by the service mgr who was out here today.
Solution? They replaced everything between the two plenums, cabinet, coil, blower, drain, etc. The dip switches were set at 400 cfm and the mfg rep said to drop it down to 350. They will be out next week to check the humidity in the living areas and of course, any leaks.
Is there something I should be asking/on the look out for?
Thanks


Reply With Quote

