Thread: 4-20 Ma
    south
    4-20 Ma
    How can i convert a 12 vdc power supply to produce 4-20 ma?
    Need something simple to test actuators and vfd signal inputs.
    I don't really want to spend the money on a fluke process meter because i don't do controls all the time.
    Aug 2000
    Buy a Kele signal generator. Think mine was about $150 a few yrs ago.
    Your poor planning does not constitute an emergency on my part!!!!
    Lewisburg, WV
    I also have one of the Kele signal generators. It works very well.
    Here is a link with more information on it
    http://www.kele.com/olcat/TE7/ASG.PDF
    Dec 2006
    Hartford, Connecticut
    I have used one from ACT. It is in the same price range as the one from Kele.
    http://www.act-solutions.com/ICC/pdfs/psg/psg_spec.pdf
    May 2008
    Norway
    Volts / Resistance = Current
    Volts / Current = Resistance
    12V / 0.004A = 3000 ohms
    12V / 0.02A = 600 ohms
    Use a potentiometer with range 600 to 3000 ohms in serial to produce the wanted current. Tho it would probably be easier to just buy the one from Kele or ACT
    Dont have good ideas if you aren't willing to be responsible for them
    Jan 2003
    You have to also take into account the impedance of the input on the device you’re testing, which will vary between devices.
    If you’re willing to whip out a soldering iron, the AD694 is a cheap IC that can do exactly what you want. With a few parts and a DC power supply (ie battery) it will drive a 4-20ma signal that will be consistent with different devices attached to it.
    Here is a diagram.
    http://forums.parallax.com/forums/attach.aspx?a=3066