    A few questions before AC/Heater install

    I have a condo, 887 sq ft. I've gotten HOA approval to go ahead.

    I have a few questions. The bid was made at least 10 weeks ago.
    Should I just call the installer and say "Go" or go over what we discussed
    and is in the contract, one more time?

    Also, all 3 contractors who are major players in my area didn't do any J calculations. They just sized it up visually. After reading a poster here
    who is in my area and went with a 1.5 ton, he said his AC worked a bit too
    hard on a really hot day. The installer I'm going with suggests a 2 ton.

    I'm going with that, as my condo is an upper unit above 2 garages. That's what he recommended. The heat really rises.

    Another thing, I'm a smoker whose trying to quit, and my unit does not vent out my cooking fumes to the roof. Should I get up and take off a register
    and wipe it to see what accumulation of smoke and cooking fumes there are?
    I hear that it's almost the same to replace the duct work in my small unit as it is to have them cleaned (which wouldn't remove smoke in the first place).
    That is..have the duct work replaced while they are there in the attic.

    I'm going with a Carrier 38HDR on my entry patio, and a Carrier Performance series for the heater. Also, I'm having a Honeywell electrostatic air cleaner installed. I'm locked into the 38HDR as that is what is in my HOA proposal, and I want that slim line unit anyways.

    I even downloaded a .pdf of the install manual for the AC. I hope they follow all the procedures in that .pdf, even tho I bet most installers don't. (runnng final tests, etc).

    I'm in San Diego, and the contractor is Avalanche Mechanical.

    Edit: I did a crude computer calculation for my 887 sq. ft. The result was 1.8 ton, hehe.
    I think that's why I should go with a 2 ton? The heat is really retained in my condo.

  2. #2
    Join Date
    Nov 2004
    Location
    North Carolina
    Posts
    443
    My guess is that you won't be getting the unit for the origonal price. 10 week's is too far out. Some contractors will honor a price for only two weeks. Everything's going up, so don't be suprised.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,168
    Electrostatic air filters are very restrictive. They slow down air flow. They should also be cleaned every 30 days.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Jan 2008
    Location
    California
    Posts
    108
    Carrier HDR is a nice unit. They were just about mandatory in Newport Beach because of low sound requirements the city had in place. Tonnage sounds right for the s.f. and San Diego.

  5. #5
    Join Date
    Mar 2006
    Posts
    254
    Quote Originally Posted by beenthere View Post
    Electrostatic air filters are very restrictive. They slow down air flow. They should also be cleaned every 30 days.
    I have 2 Freidrich $440 floor model electrostatic air cleaners that I already clean out once a month. No biggie. I'm concerned about air flow restriction with
    the AC Honeywell. Can you expand on your reply? A serious air flow restriction resulting in noise or what?

    Also, I WILL take off a register and wipe the duct with some cleaner to check the build up.

  6. #6
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,945
    If you have a 1.5 ton system in the condo now, do not have a 2 ton system put in. Your ducting will have been sized for what you have now and increasing capacity will only create problems.

    You say that; "a poster here who is in my area and went with a 1.5 ton, he said his AC worked a bit too hard on a really hot day." Just what does this mean? Even if the system operated 24/7, if it maintained the desired temperature, it was not working too hard.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,168
    Could cause coil to freeze on low load days. Could cause damage to the compressor if it restricts air flow too much.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Mar 2006
    Posts
    254
    Quote Originally Posted by RoBoTeq View Post
    If you have a 1.5 ton system in the condo now, do not have a 2 ton system put in. Your ducting will have been sized for what you have now and increasing capacity will only create problems.

    You say that; "a poster here who is in my area and went with a 1.5 ton, he said his AC worked a bit too hard on a really hot day." Just what does this mean? Even if the system operated 24/7, if it maintained the desired temperature, it was not working too hard.
    No AC has been installed here, ever. As for that other poster, he was a bit concerned because his AC struggled to keep his same sq. ft condo as mine at
    77 degrees. Granted it was 94 F outside. He's having that checked out.
    He bought a York. He also said it was during a 2 hour period that his AC
    didn't go below 77F.

    So, now...if I've never had an AC in my unit, are you saying that a 2 ton will cause problems?

    I fully understand that an AC that constantly kicks off and on uses more juice than a unit that runs steadily. I got that from this forum. But like I said in my above post...my unit retains heat. It got down to 62F at midnight last night, the high that day was only 75F. At midnight, my condo was still at 80F. Do you still recommend I reconsider and go 1.5 instead of 2 ton?
    I know there's not enough facts for you to answer fully.

  9. #9
    Join Date
    Mar 2006
    Posts
    254
    Quote Originally Posted by beenthere View Post
    Could cause coil to freeze on low load days. Could cause damage to the compressor if it restricts air flow too much.
    Great...anyone else wanna concur..lol. I can always have the cleaner installed and yank out the electrostatic Honeywell part if I wanted to. If you know about filters, the electrostatic metal part is not that retrictive. I know because it's going to be basically the same Honeywell electrostatic metal part as what I have in my 2 Friedich air cleaners right now. They aren't that restrictive.

    From previous replies to this question month ago, noone else seemed to think it was a concern. Are you saying that since my sq. footage is so small, it might be a problem? Or are you making a blanket statement about all such cleaners?

    No offence. But with the few replies I've gotten, they represent a tiny percentage of possible replies. Again, no offense...but I'm just going to have to go with my own judgement.
    Your reply is almost alarmist with very little to back it up.

  10. #10
    Join Date
    Dec 2007
    Location
    Cedar Grove, Wi-Sheboygan
    Posts
    1,582
    with his statement regarding the EAC he might have thought you had one of those already charged types you purchase from a store that are the same size of regular filters the 1" type. A regular EAC should not hinder your Static.

  11. #11
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,168
    An electrostatic air filter, is not the same as an electronic.
    An electronic is ok.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    Join Date
    Mar 2006
    Posts
    254
    Whatever, Honeywell makes an electronic air filter for Friedrich. The main part you take out and put in a bathtub once a month. I own 2 $499 ones.

    Who here is saying having one installed is a bad thing? I don't want guesses or could be's.
    How does that help anyone?

    I may have erred temporarily in terminolgy. ELECTRONIC...geesh, Honeywell.

    I doubt the participants replies have enough knowledge to actually do more than guess or give out unsubstantiated whims. Even tho there's lots of other good info here.

    One forum member says an electronic AC filter "might" restrict air flow.
    What's one member's musings compared to the millions of electronic air filters installed?

    Sometimes I wish I'd get more feedback. Not one dudes replies.

    Are ANY of you replying actual AC contractor estimators?
    Not that's a big deal, but read back my original post and reply one part at a time.

    I'm getting bits and pieces here, some useless. Hopefully, no offence.

  13. #13
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,168
    Terminology counts.
    Your terminology ask a question about one type of filter. But you really want info on another type.

    The accuracy of most answers is directed related to you asking the question about what your really getting.

    Electrostatic air filters are restrictive.
    ELECTRONIC are not.
    Unless your getting the Electronic with post filters.

    Now, which one do you really want to know about. I've sold and installed both electrostatic and electronic.(electronic with and without post filters)

    This site can do better, when asked questions with accurate info.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event