Results 1 to 13 of 16

Hybrid View

  1. #1
    Join Date
    May 2008
    Location
    Austin, TX
    Posts
    29
    Post Likes

    Evap? producing too much water?!

    Last time I asked a question here, it was for my downstairs unit. Now, my upstairs unit is causing me grief.

    The unit shuts itself off automatically because of the overflow detector found inside the drain pipe. I believe that the pipe is draining correctly, but I might be wrong. In addition, the unit seems to be producing more condensation/water than it should (otherwise why would it be shutting off after 1 minute).

    I had a tech here just last Tuesday. My pressures were good (40? I think) at the condenser. The temp drops were approx 22. This applies to both units.

    Any ideas about what is happening here? I guess the evap coil could have failed since Tuesday, but I doubt it.

    5-yo Trane XR12 5-ton.

    Any help and/or insights are greatly welcomed.

    I will likely have to call the tech again, but it helps to know what might be going on.

  2. #2
    Join Date
    Jun 2008
    Posts
    34
    Post Likes
    I don't know but 5 tons is huge! Haha. What is your footage? Just curious.

  3. #3
    Join Date
    May 2008
    Location
    Austin, TX
    Posts
    29
    Post Likes
    Thread Starter
    2600 up
    2600 down

    Yes, it's huge, but we got a fantastic deal on the house a few years back and we have enough children to fill it...

  4. #4
    Join Date
    Jan 2008
    Location
    California
    Posts
    110
    Post Likes
    Would definitely want to confirm drains indeed are clear and flowing. Depending on drain trap configuration the air turbulence at the coil drain outlet could be splashing condensation and creating a 'false-fail' effect. A loose duct could allow new moisture into space, adding to water removal. Poor airflow can increase condensation, but not enough to fill the secondary drain.

  5. #5
    Join Date
    May 2002
    Location
    Houston Texas
    Posts
    6,383
    Post Likes
    Simple enough for whatever reason you have a clogged drainline. Have a tech out and have the lines flushed and if need be have the sewer vent lines snaked out by a plumber. Have this attended to ASAP before it floods your ceiling and cost you a great deal of money and frustration.

  6. #6
    Join Date
    May 2008
    Location
    Austin, TX
    Posts
    29
    Post Likes
    Thread Starter
    Thanks for the reply. I poured a bit of clorox down the drain portion, as is annually recommended. At this point, all appears to be OK. I have a plumber's snake, but apparently am not very adept

    Just before the trap, there is an opening in the pvc line, apparently for some form of venting. I can feel water going - down the drain pipe. Can I assume this is normal?

  7. #7
    Join Date
    May 2008
    Posts
    17
    Post Likes
    already stated check that your drain line is clear.

  8. #8
    Join Date
    May 2008
    Location
    Austin, TX
    Posts
    29
    Post Likes
    Thread Starter
    A previous tech (a couple of years ago) must have removed the caps, as I found them on top of the units. I put the caps back in place. Totally makes sense how the caps are required to aid condensation flow out of the units.

    One other question. As noted, the post-evap drains both have traps and, at some point downstream, actually tee together. Near the tee, there is another opening in the PVC. This is behind BOTH traps. Should that one be capped? Does it matter; are there pitfalls; etc?

    Thanks again.

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,635
    Post Likes
    it should be just after the traps. that can be a hazzard if its not high enough. If the drain cloggs after it, it could allow water to over flow and damage your ceiling.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Join Date
    Jun 2008
    Location
    west point, ga.
    Posts
    328
    Post Likes
    If there is a tee before the trap it is to clean and treat the trap and it does have to have a cap on it.

    The tee after the trap is a breather and no it does not have to be caped but as stated it has to have a pipe coming off the top higher than the drain itself.

    Make sure to keep drains treated once a month.

  11. #11
    Join Date
    Jan 2008
    Location
    Dothan, Alabama
    Posts
    25
    Post Likes
    I would check to see if the unit is double trapped causing vapor lock. No such thing as to much condensation . That just proves your evaporator is removing heat and humidity. You just need it to flow out.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.