    Leak at air handler

    New Rheem Contour/AC unit, matched coil. Arzel-zoning with bypass. Works great, but with several humid 95 degree days in a row it started to get small amounts of water leaking out as shown - I checked and nothing is leaking from above, and the condensate drain doesn't appear clogged. There are no leaks on our more usual 80-85 degree days. Should I be concerned? Doesn't seem right it should leak, ever, but the conditions under which it does are so unusual for here that I can tolerate it if need be. I'm guessing it's related to icing of the coil which is worsened by the bypass damper recirculating already-cooled air (zones are relatively small). Note: I did check the line piping and entry to the unit and it was not sweating or dripping.

    I know I should contact the dealer, but I'd expect "it looks fine to us now, can't figure it out unless it does it again" - of course it will only do it again during an unusual heat wave and they'll then be so busy they can't get out while the problem is there!

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    71,865
    Post Likes
    Could be a slight restriction in the drain line.
    Could be air leaking at the panel cover.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    If it only does it on certain types of days, my "GUESS " is that the unit is sweating, due to insulation missing/air leakage as said before. With the txv I doubt the coil is icing....call them back and show them your pics.
    If everything was always done "by the book"....the book would never change.

  4. #4
    Join Date
    Sep 2007
    Posts
    32
    Post Likes
    Well, there indeed is an air leak on the cover edge in the same region. I used silicone caulk on it, hopefully that's solved (until someone needs to take the panel off, but the silicone should be easy to deal with).

  5. #5
    Join Date
    Jun 2008
    Location
    Phoenix, AZ
    Posts
    70
    Post Likes
    I've seen a lot of units having sweating pipes that arent positioned properly over the drain pan and/or they are touching the outer panel. This will cause a very slow drip. If the condensate was clogged you'd have a lot of water. Just adding to other posts with air leak being possible also... goodluck!