Thread: Analize This AC Preformance
-
06-27-2008, 07:41 PM #1
Analize This AC Preformance
Do you ever work on your own stuff at home?? well I don't that often haha! I gotta say I have limited experience with Residential A/C. My system here at my place I don't think is doing that good of a job at cooling the place here, Yesterday it wouldn't even drop below 80*F where the stat is located, even with the temp outside yesterday around 85F and a bit of sun on 3 bigger windows with blinds closed it couldn't keep up. zoning issue maybe?
I'm going to pass on some info and we'll see what you guys think about this contraption!
R-22
Unit: Carrier M#38CK01834 (1.5ton??)
Coil: Custom Coils Inc. M#SA6979 (btu's ??)
Air handler: Temp Mizer High Velocity M# HV-52H 650CFM
Metering Device: Inline Orface
Measured at Condensing Unit
Suction: 67psi @ 42F(low superheat?)
Liquid: 210psi @ 97F
Condenser Air: 84F in, 95F out
Evap Air: 78F return, 61F Supply
Bristol pump M#H29B16UABCA OC 25
241V at contactor, 5.3A(@67psi suction)
MikeSig removed by mod. G-Rated site
-
06-27-2008, 07:57 PM #2
Slightly undercharged? What's your target SH?
-
06-27-2008, 07:58 PM #3
Professional Member
- Join Date
- Apr 2007
- Posts
- 6,286
-
06-27-2008, 08:58 PM #4
if you got 17 degrees drop across evap coil you should be cooling. any heat gain?
"When the people find they can vote themselves money,that will herald the end of the republic" - Benjamin Franklin
"Government is not reason, it is not eloquence, it is force;like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action"- George Washington
-
06-27-2008, 11:15 PM #5
What is the sq ft of the area being cooled?
A 17 degree split is good and you arent undercharged by much with those system pressures
-
06-28-2008, 11:19 AM #6
I liked the 17 degree drop, but like i mentioned earlier i think it's just air distribution(i said zoning) and yeah i think the evening sun in the front windows are a bit of heat gain, and this is the room the stat is located. Probably nothing I can do. Space is just under 1200sq ft.
I'm not a fan of a fixed metering device and i was thinking of removing it and slapping in a TEV and a small reciever after the condenser. Think I would get better efficiency out of this or would it increase the load on the condenser. Or would it work OK i wonder. I'm sure i'd have to throw a potential relay and a start cap on the PSC compressor aswell. I may get bored haha!
MikeSig removed by mod. G-Rated site
-
06-28-2008, 01:10 PM #7
Professional Member
- Join Date
- Dec 2007
- Posts
- 89
Check Ur Filter!:d
-
06-28-2008, 01:48 PM #8
-
06-28-2008, 03:00 PM #9
superheat= maybe 4*
Might want to undress that evaporator and check it for dirt.If you get pressures up to maybe 76psig and superheat doesn't change then I would check coil for metering problem."Everyday above ground, is a good day".
"But everyday that you have made a difference in someones life, may insure you stay above ground a little longer".<aircooled>
-
06-28-2008, 03:22 PM #10
Professional Member
- Join Date
- Jun 2006
- Posts
- 294
Get the cfm, the supply and return WB temps to get delta h to determine the actual system cooling.
-
06-28-2008, 03:25 PM #11
Professional Member
- Join Date
- Apr 2007
- Posts
- 6,286
http://efficientcomfort.net/jsp/PsychroCoilCalc_Web.jsp
Get CFM wb and db entering and exiting evap. then use that calc above.
-
06-29-2008, 03:37 AM #12
this is the info I like to see,

My CFM is 650 and I'll get some temps. DB temps I have but to get some WB temps just put my Digi thermometer probes in a wet rag and and take a reading, how do you guys get your WB readings with basic tools?
mikeSig removed by mod. G-Rated site
-
06-29-2008, 07:05 AM #13
Digital sling.


Reply With Quote
, yip she's new, lol