    fluttering gauges

    Why would gauges flutter?

  2. #2
    Join Date
    Oct 2006
    Location
    Springfield, Clarksville. Tn
    Posts
    37

    Could be bad..

    Valves not seating properly, Vibration
    Ken

  3. #3

    Smile

    Thanks

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,785
    Non condensables/contaiminates in the system.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5

    Red face

    Quote Originally Posted by beenthere View Post
    Non condensables/contaiminates in the system.
    So would I have to flush it out with r11 or just change dryer and new refrigerant

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,785
    More like recover, install new filter drier, vac, and virgin charge.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Flush with R11? Whaaaat?
    ___________________________________________


  8. #8
    Join Date
    Jun 2008
    Location
    va
    Posts
    800
    Questions......New start up? Old unit? Is the system working correctly or close? Guage readings and indoor and outdoor temps? Both low and hi sides fluttering?

  9. #9

    Smile

    Quote Originally Posted by beenthere View Post
    More like recover, install new filter drier, vac, and virgin charge.
    Didn't word it rite but that's what I ment. thanks

  10. #10
    Quote Originally Posted by machery View Post
    Questions......New start up? Old unit? Is the system working correctly or close? Guage readings and indoor and outdoor temps? Both low and hi sides fluttering?
    It's an old unit, it's working ok, guage reading low side 55 high side 265, indoor temp. 87 outdoor temp. 83, only high side flutter.

  11. #11
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Check filters and condenser coil for cleanliness....... thats all I'm gonna say outside the tech forum.
    ___________________________________________


  12. #12

    Hmm

    Quote Originally Posted by DPSwitch View Post
    Check filters and condenser coil for cleanliness....... thats all I'm gonna say outside the tech forum.
    Changed filters and acid wash coils recently

    Thanks for your input

  13. #13
    Join Date
    Mar 2007
    Location
    Madison, Wisconsin
    Posts
    2,263
    Apply for pro membership.
    I r the king of the world!...or at least I get to stand on the roof and look down on the rest of yall

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event