  1. #1

    fluttering gauges

    Why would gauges flutter?

  2. #2
    Join Date
    Oct 2006
    Location
    Springfield, Clarksville. Tn
    Posts
    37

    Could be bad..

    Valves not seating properly, Vibration
    Ken

  3. #3

    Smile

    Thanks

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,370
    Non condensables/contaiminates in the system.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5

    Red face

    Quote Originally Posted by beenthere View Post
    Non condensables/contaiminates in the system.
    So would I have to flush it out with r11 or just change dryer and new refrigerant

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,370
    More like recover, install new filter drier, vac, and virgin charge.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?