  1. #14
    Join Date
    Jun 2008
    Posts
    11
    Quote Originally Posted by smokin68 View Post
    Smart. Get a tech to check it out. It can be anything from a compressor to a shorted wire. All you'll get here are guesses. Prepare for the worst, hope for the best.
    I guess that's what i'm gonna have to do considering home warranty won't fix it.

  2. #15
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,548
    You have a home warranty and they won't fix it? What reason did they give you?
    If everything was always done "by the book"....the book would never change.

  3. #16
    Join Date
    Jun 2008
    Posts
    11
    Quote Originally Posted by smokin68 View Post
    You have a home warranty and they won't fix it? What reason did they give you?
    They have given me all kinds of reasons as to why they can't fix it. The outside unit is a 3 ton unit and the inside is a 4 ton. The ac tech said they are not compatible.

  4. #17
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,786
    Post the mod numbers of both units.
    Some one may be able to verify either way if that is a match.
    Some brands did use larger indoor units then outdoor units.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #18
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,512
    that tech that said that could could very well be full #### a 4 ton drive furnace on low speed blower could be just right and the oversized coil should not be a problem . there is a possibility that it could be a properly matched system

  6. #19
    Join Date
    Jun 2008
    Posts
    11
    Quote Originally Posted by beenthere View Post
    Post the mod numbers of both units.
    Some one may be able to verify either way if that is a match.
    Some brands did use larger indoor units then outdoor units.
    where do you find the mod numbers?

  7. #20
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,786
    Depends a little on brand.
    OD unit, look near where the copper lines attach to it. Probably just above them.
    ID unit, look around where the lines attach also.
    If you also have a furnace, it should be inside the access panel.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #21
    Join Date
    Jun 2008
    Posts
    11
    Quote Originally Posted by beenthere View Post
    Depends a little on brand.
    OD unit, look near where the copper lines attach to it. Probably just above them.
    ID unit, look around where the lines attach also.
    If you also have a furnace, it should be inside the access panel.
    Thanks I'll go check it out.

  9. #22
    Join Date
    Jun 2008
    Posts
    11
    OK Found the numbers..
    OD Coleman cooler 10
    model number BRCQ048B
    Factory charge 5.13 oz

    ID Nordyne
    model number CIQA-036U-B
    charge 1 oz

    Think I found the problem.. They OD unit specifies a 40 amp breaker. the breaker that keeps flipping is a dual 30 amp breaker!

  10. #23
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,786
    Good. Because that is a bad mismatch.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #24
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,512
    you need a new matched system

  12. #25
    Join Date
    Jun 2008
    Posts
    11
    Quote Originally Posted by beenthere View Post
    Good. Because that is a bad mismatch.
    the units don't match?

  13. #26
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,512
    beenthere you type to fast for me to keep up

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event