06-28-2008, 09:44 AM #15
You have a home warranty and they won't fix it? What reason did they give you?
If everything was always done "by the book"....the book would never change.
-
06-28-2008, 09:51 AM #16
Regular Guest
- Join Date
- Jun 2008
- Posts
- 11
-
06-28-2008, 10:02 AM #17
Post the mod numbers of both units.
Some one may be able to verify either way if that is a match.
Some brands did use larger indoor units then outdoor units.
-
06-28-2008, 10:08 AM #18
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,714
that tech that said that could could very well be full #### a 4 ton drive furnace on low speed blower could be just right and the oversized coil should not be a problem . there is a possibility that it could be a properly matched system
-
06-28-2008, 10:11 AM #19
Regular Guest
- Join Date
- Jun 2008
- Posts
- 11
-
06-28-2008, 10:14 AM #20
Depends a little on brand.
OD unit, look near where the copper lines attach to it. Probably just above them.
ID unit, look around where the lines attach also.
If you also have a furnace, it should be inside the access panel.
-
06-28-2008, 10:15 AM #21
Regular Guest
- Join Date
- Jun 2008
- Posts
- 11
-
06-28-2008, 10:26 AM #22
Regular Guest
- Join Date
- Jun 2008
- Posts
- 11
OK Found the numbers..
OD Coleman cooler 10
model number BRCQ048B
Factory charge 5.13 oz
ID Nordyne
model number CIQA-036U-B
charge 1 oz
Think I found the problem.. They OD unit specifies a 40 amp breaker. the breaker that keeps flipping is a dual 30 amp breaker!
-
06-28-2008, 10:30 AM #23
Good. Because that is a bad mismatch.
-
06-28-2008, 10:30 AM #24
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,714
you need a new matched system
-
06-28-2008, 10:32 AM #25
Regular Guest
- Join Date
- Jun 2008
- Posts
- 11
-
06-28-2008, 10:32 AM #26
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,714
beenthere you type to fast for me to keep up



Reply With Quote