No condensate from HVAC drain
I am a first time homeowner of a 45 year old ranch with a 22 year old HVAC, and the condensate line drain for the AC is dry, although the 22 year old system is working. The outside condenser is clean, but does seem to run a lot, inside filter is replaced at regular frequency. I do have a dehumidifier running in the basement, collecting over 1.5 gallons/day, but the independent humidistat in the basement averages about 70%. At first I thought it was a clogged line, but it is not. How do I without knowledge of HVAC systems or local contractors/service personnel depend on their assessment, as the system is functional--but AC without condensate??? Doesn't make sense to me. Any ideas, how does one approach the problem if there is one? Central Illinois humidity without condensate...? Thanks. John.
-
06-26-2008, 06:33 AM #2
What are your systems pressures?
sounds like you are low on refrigerant
-
06-26-2008, 06:53 AM #3
Maybe your just looking at the wrong drain line. Many system have a primary drain that connects to the plumbing. The secondary normally goes outside. If you are looking at the secondary, you should hope it never drains from there.

-
06-26-2008, 01:47 PM #4
New Guest
- Join Date
- Jun 2008
- Posts
- 2
There is only one drain line to the stand pipe adjacent to the HVAC system. It's a clear flexible tubing that starts from the pan at the bottom of the evaporator coil and runs to the stand pipe, a distance of maybe 4'.
As far as pressures go, I do not have the equipment to check them. But if I'm understanding correctly, you are thinking that I'm getting minimal cooling from the system running a lot, and the stand alone dehumidifier is acting like a slave unit because the system may be low on refrigerant? FYI The stand alone dehumidifier is set to run constantly on high.
-
06-26-2008, 02:25 PM #5
Professional Member
- Join Date
- May 2008
- Location
- Clovis/Fresno CA
- Posts
- 193
what is the humidity in the house? is the unit cooling right? maybe there is'nt that much humidty in the house so the evap won't hold on to it . There are to many factors to look at with your minimal information
-
06-26-2008, 02:30 PM #6
Required Trouble Shooting Data
My advice: get a low cost humidity gage at a local hardware store & see what the percentage-RH is in your home, I can cross-reference that to the wet bulb depression.
TROUBLE SHOOTING DATA
Age a unit & EER or SEER Rating ________
SF of home & major city near you __________
Outdoor temperature: _____________
Outdoor condensers DB discharge-air-temperature ___
In-Door temp DB and WB: ___________
Air Handler's Total-ESP: _____________
Suction-Vapor line temperature: ____________
Liquid line temperature: ______________
Superheat & Subcooling: _____________
Return air temp DB and WB, or %RH: ____________
Supply air temp DB and WB, or %RH: ____________
If you want meaningful help, provide us with most, if not all, of the above EASY TO TAKE data.
Then perhaps, we can ballpark an opinion on what the unit is doing.
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
06-26-2008, 07:38 PM #7
Professional Member
- Join Date
- Jul 2004
- Location
- NJ
- Posts
- 44
He said the outdoor unit seem to run alot, betcha the condenser fan is turnin, but the compressor isn't, no compressor, no cold evaporator, no condensation.
"Peace cannot be kept by force; it can only be achieved by understanding." Einstein
-
06-26-2008, 08:11 PM #8
Is it maintaining temp.
If your basement is humidistat is reading 70%RH, and your getting less then 2 gallions of water a day from your dehumidifier. Either the humidistat is wrong, or your dehumidifier isn't working right either.
What temp do you set your thermostat for, and does it maintain that temp.