Results 1 to 13 of 15
Hybrid View
-
06-25-2008, 01:12 PM #1
Professional Member
- Join Date
- Jun 2008
- Location
- South,Tx
- Posts
- 323
For those Pros out there, reading a Flowrator S.H and Sub-cooling
How is it when i go on S.C. i allways have problems reading S.H. and Sub-cooling with a flowrator system , and its not as accurate a TXV.
Some one give some ideas about this , and how to go about it !
Matt 7:12 The Golden Rule
"Do for others what you would like them to do for you. This summary of all is taught in the law and the prophets.
-
06-25-2008, 01:23 PM #2
No idea why you have trouble.
Don't know what you mean not as accurate either.
-
06-25-2008, 01:40 PM #3
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
You gottta re word that a little differently. It's not clear what you mean.
-
06-25-2008, 01:47 PM #4
Professional Member
- Join Date
- Jan 2002
- Posts
- 42
a TXV - use sc to maintain a collum of liquid at valve and constant evap sh, caps and flow devices - use sh which is dependant on condenser pressure for flow, greater cond pressure greater mass flow. Question a little unclear hope this helps
-
06-25-2008, 01:47 PM #5
Professional Member
- Join Date
- Jun 2008
- Location
- South,Tx
- Posts
- 323
Matt 7:12 The Golden Rule
"Do for others what you would like them to do for you. This summary of all is taught in the law and the prophets.
-
06-25-2008, 02:02 PM #6
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
-
06-25-2008, 02:04 PM #7
A fixed metering device system will sometimes hunt when its low on charge.
It also appears to hunt sometimes after the coil has been frozen. Due to oil having been washed out of the compressor, and now moving through the evap.
Have you applied for pro membership yet.
These are question that are more technical in nature then we should be going into in the open forums..
They may close or delete it soon.
-
06-25-2008, 02:08 PM #8
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
-
06-25-2008, 02:11 PM #9
-
06-25-2008, 04:14 PM #10
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
Not so sure hunting is a word that I would use in conjunction with a fixed bore metering device.


Reply With Quote