Results 27 to 39 of 62
-
06-25-2008, 05:08 PM #27
Professional Member
- Join Date
- Jun 2008
- Location
- va
- Posts
- 800
If it's a 22 to 410 change-out, the line set GETS CHANGED unless it's absolutely prohibitive, then it gets flushed with the Rx11. No chances or risks taken if avoidable.
-
06-25-2008, 05:27 PM #28
Regular Guest
- Join Date
- Jun 2008
- Location
- Northern Virginia
- Posts
- 34
Seems to make sense to me based on this thread and forewarned is forearmed.
If I did not open this thread this morning and the installer reused the lines tomorrow, as specified by the contractor/engineer in the proposal, who bears the cost of replacement/reinstallation down the road if a problem pops up? Who should bear it?
What steps should the homeowner take to reduce his exposure if the installer uses a "controversial" installation method, specifically reuse of R22 line (irregardless of cleaning mechanism) vs replacement? If the extended warranty is not the correct instrument then what is?
-
06-25-2008, 06:38 PM #29
Foolow manufacturer install instructions.
-
06-25-2008, 06:47 PM #30
Regular Guest
- Join Date
- Jun 2008
- Location
- Northern Virginia
- Posts
- 34
I'm not communicating something well I guess.
How does the homeowner determine if the manufacturer's install instructions have been met? In this example, what are Carrier's install instructions?
As I have said above, the installer appears to be planning on reusing the existing lines, knowing full well that the old set is R22 and that the new set is R410a.
I fully plan on being down in the basement with the installer the entire time, but other than a few specific items I have read about here I will have no idea what to ask him or if he is doing what he says.
How do I determine if the manufacturer's install instructions have been met? How do I protect myself from the installer failing to comply with the manufacturer's install instructions?
"Pick a good installer" is certainly insufficient because what that usually means is "Pick an installer as good as me"; neither recommendation actively protects the homeowner from installer error.
-
06-25-2008, 06:55 PM #31
Carrier doesn't require new line set. I believe they are the one that doesn't want RX11 flush used either, just a nitro blow out.
Ask the installer what the install instructions say about re using the old line set.
Its your system, your money.
-
06-25-2008, 08:24 PM #32
The horizontal run of the lines are critical because they can form oil pockets (Per Lennox Tech Support). Replacing the horizontal section of the lines and clearing the lines with dry nitrogen is also an option.
IMHO the flush does a better job, but both ways are proven to work if done correctly. The dollar amount is close either way as long as the horizontal section (line set) is a reasonable distance.
-
06-25-2008, 08:37 PM #33
Is it that hard to change your line set? if everything is accesable then i don't understand why you wouldn't want to. half the line sets i run dont even need a full roll and can be done with leftover from the last job( provided it was sealed after being cut). i have done a bunch without changing it where it could not be done without cutting open walls, and have not had a problem yet, but we take extra precations. but if it can be done, why not do it? you're spending enough as it is, why cheap out now?
-
06-25-2008, 08:55 PM #34
-
06-25-2008, 08:59 PM #35
Professional Member*
- Join Date
- May 2007
- Location
- DC Metro area
- Posts
- 3,223
What's the typical course of action you guys take when there is a finished basement with refrigerant lines under the wall? Do you typically just leave it and flush it, or have you ever cut portions of the drywall out to "fish" the lineset through?
-
06-25-2008, 09:14 PM #36
Member
- Join Date
- Oct 2006
- Location
- Emerald Coast, FL 30.1N 85.8W
- Posts
- 681
Nitro purge & evac should do it
blowing out the line sets & evacuating the system should be fine. I also installed a drier before the txv.
I have a small temperature drop on the driers, probably from the oil mixture, but it isn't bad. I plan to remove the drier downstream of the txv & replace the liquid line drier during PM next March.
For me, it's a lot more cost effective to do a pull down & change driers than buy a line set & put it in.
-
06-25-2008, 09:29 PM #37
-
06-25-2008, 09:46 PM #38
emcoasthvacr, You think it is more cost effective to go back and change driers, than just using the proper method of rx11 flush! Is it really that difficult and expensive to do it right? You readilly admit that you think you have seen some signs that you are mixing the oils, but what the hell , its just a little temperature drop across driers! Whats next, ditching the vacum pump, it would save you time, and lets face it, those vacum pumps are not cheap, its only a little moisture/non-condensables, I know we can just change the driers out at pm time. COME ON!
-
06-25-2008, 10:05 PM #39


Reply With Quote
. Us bottom feeders don't know all them nifty tricks
