06-25-2008, 10:05 AM #27
Professional Member
- Join Date
- Aug 2003
- Posts
- 466
Once a technician gets comfortable with taking superheat and subcooling measurements, that technician will never again even think about diagnosing a system without that important data. Knowing superheat and subcooling of a system is like being able to see inside of the system. For example; if your superheat on a fixed metering system is in line but your subcooling is high but your head pressure is not out of line, there is a restriction in the condensing side of the system that needs to be taken care of. Once you are used to taking superheat and subcooling measurements and you understand what those numbers tell you about the operation of the refrigerant system, your eyes will be opened to a whole new dimension of troubleshooting.
-
06-25-2008, 10:11 AM #28
Professional Member
- Join Date
- Jun 2008
- Posts
- 35
Digital Device For Sh And Sc
I know the importance of it. I just am not comfortable. i want the quickest way to get the reading. I will pay for a device if needed, just not sure if it is worth it. Any feedback on using digital device to measure superheat & supercool vs old manual approach
-
06-25-2008, 10:17 AM #29
A clamp-on thermocouple for measuring superheat/subcooling is your friend. Get one, use it, love it.

As for digital stuff, if I was still in a service truck I'd get a set of Digicool gauges or the Testo equivalent and thereby have what I need to accurately measure saturated temps and superheat/subcooling. As it is I do have a superheat/subcool meter/calculator by Fieldpiece, which works decently. Always good to have a backup in case the first line of whizbang defense fails, so I also can measure line temps with a separate meter.
-
06-25-2008, 10:20 AM #30
-
06-25-2008, 10:25 AM #31
Professional Member
- Join Date
- Jun 2008
- Posts
- 35
shophound. I agree it is worth it to measure superheat. I just want a little insight into whether it is worth to buy a mini-computer that automatically measures the superheat/supercool for you. Sounds the others like manual with a clamp for the suction line. What do you think.
-
06-25-2008, 10:42 AM #32
Professional Member
- Join Date
- Apr 2007
- Posts
- 6,286
For speed when time is money it's worth it.
Fieldpiece has a dual thermometer the ST-4 it has dual inputs and is adj. for accuracy....very easily adjustable.
The clamps are a little expensive @ about $40 a piece......Once you get those you'll hate the old method. Obviously the Digicool gauges or Testo gauges are top of the line and are well worth it to the folks that want speed accuracy and want it all digital.
P.S. Hey Shophound I sure have been seeing a lot of the educational committee commenting again.....and this strange little # countdown under jrbenny's name.......anything you guys are talking about ?
-
06-25-2008, 10:57 AM #33
Let's see...carry a PT chart, a notepad and pencil, manifold gauges, a separate meter to measure the pipe temps, and a pipe clamp thermocouple vs. carrying at maximum my gauge manifold and a superheat/subcooling meter/calculator or minimum a digital manifold with onboard superheat/subcooling calculation...hook up the gauges to the schraders, clamp onto the pipe I want to monitor, rock n' roll.
Since I'm not in the speedy end of the trade, I do good by manifold gauges and the Fieldpiece device/pipe clamps. If I was in a service truck I'd definitely be thinking about Digicool or Testo. The easier it is to do, the more likely you are to do it...every time.
-
06-25-2008, 11:00 AM #34
-
06-25-2008, 12:25 PM #35
Professional Member
- Join Date
- Jun 2008
- Posts
- 35
hey shophound are you telling me to get my pro membership cause i hit 15? not sure I understand your last posting
-
06-25-2008, 12:32 PM #36
Regular Guest
- Join Date
- Jun 2007
- Location
- The Twilight Zone
- Posts
- 2,964
-
06-25-2008, 12:33 PM #37
You should apply for pro membership if you're in the trade, and that can be verified by the membership committee. Having pro membership will give you access to the pro technical forum, and the new educational forum, which should be coming online soon. Between the pro technical forum and the educational forum, you will have a wealth of information about HVAC theory, repair scenarios and problems, etc.
-
06-25-2008, 07:45 PM #38Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
06-25-2008, 07:54 PM #39
Regular Guest
- Join Date
- Mar 2007
- Location
- media,pa
- Posts
- 80
pro forums
i will try to apply once i can find all my stuff. e.p.a certified,will have to scan my card. can't find my r.s.e.s. cert's. will this have any real bearing on the decision to make me a pro member.


Reply With Quote