  1. #14
    has a large one, right now. i do suspect a burn thats why filter and acid away. i guess it must have stopped up the tubes and got the other compressor. i think im going to try blowing her out again in the morn. if no luck there, will price header assembly.

  2. #15
    Join Date
    Nov 2007
    Location
    Charlotte,nc
    Posts
    15
    Don't know the size of the unit, and don't know if you have replaced a header but, it is much easier to replace the evaporator coil if it is found to be clogged tubes, once again it happens in heating, and should clear out and trap in the liquid line drier, when the heat was cycled, Had a clogged header on a 3.5 carrier 6years ago when I changed a compressor, but it was ac only, Changed 2 headers in 2 seperate carrier units, back when carrier first came out with metering devices crimped in the header and I swore never to replace another header again. The ones I changed the pistons where not crimped tightly from the factory and they came out

  3. #16
    Join Date
    Apr 2007
    Location
    Philadelphia
    Posts
    2,192
    Quote Originally Posted by red949597 View Post
    one hour vacum, nitrogen to 250, held fine, one hour vacum weighed in charge 11 lbs.
    One hour vacuum??? Thats a good reading to you huh?
    Call the manufacturer and tell them that.

  4. #17
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,814
    When you noticed the temperature change or frost line at the suction drier, you most likely located the restriction.

    Let us all know how you come out.
    God Bless our Veterans

    God Bless the USA

  5. #18
    Join Date
    Apr 2007
    Location
    Philadelphia
    Posts
    2,192
    When you tried it in heat mode were you still taking the suction pressure close to the compressor?
    also put a drier in with a access port on it so you can take pressures on either side of it.
    What does the evap coil/filter/blower wheel look like, and crazy question. ARe you SURE the fan was running???? If so where the amps close to FLA?

  6. #19
    Join Date
    Oct 2007
    Location
    Southern Indiana
    Posts
    94
    You say you pulled a one hour vacuum? Did you have a micron gauge on it?
    Sounds like you have moisture in the system freezing up and causing a restriction. Purge with nitro, then pull another vac. using a micron gauge.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event