    1.5t Goodman Heat Strip Sizing

    Trying to get correct heat strip sizing for Goodman 1.5 ton 15 Seer Heat Pump system for new construction 900 square foot home in NE Oklahoma. All electric home. Heat Load Load Calculation results:
    16261 btu Heat Loss
    11000 btu Heat Gain
    15000 btu Actual House Distribution.

  2. #2
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    Ummm......you don't know the watt to btu conversion?


    Your HVAC contractor should know that one pretty easily.

  3. #3
    Join Date
    Jun 2008
    Posts
    11
    Post Likes
    Thread Starter
    I've had 2 different contractors come on site and give me 2 different opinions on heat strip sizes...just trying to get more advice here...thanks for answering a question with a question.

  4. #4
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    What did your contractors offer? And what was the reasoning behind their choices.



    Sorry it kinda sounded DIY'er to me which is against the rules.

  5. #5
    Join Date
    Jun 2008
    Posts
    11
    Post Likes
    Thread Starter
    One tech said 5kw and the other said 7.5kw for a faster recovery. I don't know anything about it really. DIY is out of the question because I don't really know enough about this stuff to try and tackle it myself..If I did I would not be asking the questiom, but thanks for flattering me. Antone else want to try and help?

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Ductwork in unconditioned space, 7.5KW
    Ductwork in conditioned space, 5KW

  7. #7
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    You'll learn if you keep coming here the more info supplied the better and more informative answer you'll get. Welcome to the site sorry to make it a poor experience.

    Beenthere is the one to listen to.

  8. #8
    Join Date
    Aug 2003
    Posts
    466
    Post Likes
    We simply don't know your circumstances well enough to make a really informed decision for you. Since there are 3,413 Btu's per KW of electric resistance heat at 240 volts input of electricity, a 5KW heater would provide about 17,000 Btu of heat which is more then your total estimated heat loss. Therefore, you should never need more then a 5kw heater if you are operating at 240 volts of electrical current.

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by everythingair View Post
    Therefore, you should never need more then a 5kw heater if you are operating at 240 volts of electrical current.
    What if his ductwork is in unconditioned space???

  10. #10
    Join Date
    Jun 2008
    Posts
    11
    Post Likes
    Thread Starter
    The ductwork will be in the attic.

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Then you will need to allow for the heat that the duct will lose in the attic. Depending on the amount of duct, its insulation, and the temp in the attic. You could lose 1800 plus BTUs. So a 5 KW won't be enough to heat the house if the heat pump were to break down at outdoor design temp.
    But a 7.5 can.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •