    Cool New Carrier straightcool

    What do you guys think about a spilt carrier straight cool, that has been vac and micron gauged, with a weighed in charge put in, but only has a 10 degree split at the evap coil? Subcool was ~40 degrees with ~8 degrees superheat. I tried to purge the unit to lower the subcooling to 16 then to 10 then 6 degrees but has no effect on the temp. split. No restrictions in filter drier, so does it have to be the TXV or is there another option?

  2. #2
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    You are not telling us what the actual pressures were.
    I don't know how you could purge from 40-F to 6-F Subcooling. (?)

    How much airflow do you have & how high is the humidity.
    Could it be pulling hot moisture laden air from the attic into the return.

    At 400-cfm per/ton of cooling, an 80-IDB & 74.5-IWB will produce around a 10-F SA/RA delta-T split. What were indoor conditions?


    Maybe the airflow is 475 to well over 500-cfm per/ton of cooling, it can happen with wrong speed selections, & the new powerful & sometimes oversized air handlers.

  3. #3
    Join Date
    Jun 2008
    Location
    Phoenix, AZ
    Posts
    70
    Post Likes
    Thread Starter
    Humidity is low as I am im phoenix, arizona. pressures were on the low side 53 degrees or ~135psig and 135 degrees on the high side or ~500psig. After I put some 410a into my recovery tank to get the subcooling down pressures were at 125/420 indoor was 81, outdoor was 118

  4. #4
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    What model and serial number?

    Might want to do a static pressure versus temperature test to see that the refrigerant is pure.

  5. #5
    Join Date
    Jun 2008
    Location
    Phoenix, AZ
    Posts
    70
    Post Likes
    Thread Starter
    I thought the person who did the start up left nitrogen in the unit or ... so I pulled a good vac and weighed in my charge.. the right way or so I think.. both the condenser/coil are 6 months old... model number coil CNPVP6024ACAAAA, condenser 24ABA360A320, the unit next to it is identical.

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    R410A at 135 PSIG has a sat temp of roughly 48°F.

    Get all the readings, not just is was 135 psi suction line.
    Also need all the temps.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •