06-21-2008, 09:00 PM #27
06-21-2008, 09:04 PM #28
Let me know how that comes out....I have had my eye on the YJ too! Mine put the wood to a fieldpeice the other day!
I need a new signature.....
06-21-2008, 09:07 PM #29
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
06-21-2008, 09:10 PM #30
Maybe I just got a bad one. It seems to eat batteries.
06-21-2008, 09:16 PM #31
06-21-2008, 09:18 PM #32
06-21-2008, 09:25 PM #33
IMHO only a HACK would pull a vaccum on a system w/out checking the micron level . That is truely the only way to be 100% sure that you have zero leaks and that the system is contaminent free .
Again just my opinion
06-21-2008, 09:36 PM #34
No return.
- Join Date
- Jul 2006
- Location
- Posts
- 6,058
06-21-2008, 09:45 PM #35
If you work for me and don't use your micron gauge, you'll be finding a new employer.
Merry Christmas
06-21-2008, 09:47 PM #36
NOPE !! Positive pressure can and WILL lie to you , a standing micron reading of 500 or less WILL NOT lie to you !!! There is no arguing with that !!!! I have seen it more than once . Oh and for all of you that do not use a micron gauge , when your gauge on your manifold gets to 30"hg your actual micron level can be 5,000+ !!!
06-21-2008, 09:51 PM #37
I 'm the only one at the company , that has one.That's why I take longer on repairs and find more tubes not metering or txv failures, due to no vacuum or not long enough vacuums. Nitrogen is used allot but, when you dry a system you have to remove non-condensibles .
"Everyday above ground, is a good day".
"But everyday that you have made a difference in someones life, may insure you stay above ground a little longer".<aircooled>
06-21-2008, 09:54 PM #38
No return.
- Join Date
- Jul 2006
- Location
- Posts
- 6,058
06-21-2008, 09:57 PM #39
I don't need a micron gauge I have a pressure switch on my pump that shuts my pump down at a 500 microns.