    need help with r410a Sanyo unit.

    Ok this is my first real post on this forum. i am certified in 410, but havnt been in the field for awhile. This is a super new 40,000 btu mini split, with dc inverter. So heres the run down. leak checked the system up to 600psi. evacuated it. everything good. it has 50 foot line set 100 foot total. opened up the king valves. put it to test run and ran for ten minutes no problems. put it to full cool, 95* day with my 410 gauges connected. this system has a service port on both liquid and gas. my temps are, ambient 95* suction 40* liquid 80* and 110* right out of the compressor. my high side gauge is reading 230 psi. and 130 135 psi on the suction. the evap is blowing out at about 45*, the indoor temp is 85*. no short cycle no freezing. all is pointing to a low charge, but everything else seems to be running the way its designed. the system is pre charged to 7.9 pounds and is good for 10-100' line set. im rusty on 410 its been about 2 years since i graduated. ive been reading through my text book, and i just want to make sure that it is most deff a low charge.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,789
    You vapor sounds a little low, but not bad.

    Some of them your better off leaving run for a longer time before ceciding if its low or not.
    Also, I still think your metering device is outside with that model also, so that may not be a true liquid pressure.

    Check the manual.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    partially gas and liquid, thats what i was reading. thats why i didnt want to follow the text book pressure data. im not sure with these new systems.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,789
    Might want to go to a class on ductless splits.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    well can anyone help me out with a forsure? is the head pressure less due to the way the unit works? do you usually only check suction?

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,789
    On ductless splits, usually just check vapor.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?