    hvac preswures acting strange

    4 ton unit blowing hot air ,heat coils not on ,low side pressure 68, high side 225-230 What goes with this

  2. #2
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    sounds like a bad tech is what goes with it...........

    good luck. This is not a DIY forum.
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  3. #3
    Join Date
    Jan 2005
    Location
    Ft. Worth Texas
    Posts
    4

    pressure acting strange

    may sound a little DIY to you and yes I've heard that the Texas techs are a little squirrely but in this case I was looking for a serious answer, I own my on stupid company of stupid techs but I do know how to read a manometer and a temperature gage so you don't know either huh stan

  4. #4
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    The compressor oil needs to be changed
    ___________________________________________


  5. #5
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Question.....how much refrigerant did you add to get it to that?
    ___________________________________________


  6. #6
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Quote Originally Posted by stangarner View Post
    may sound a little DIY to you and yes I've heard that the Texas techs are a little squirrely but in this case I was looking for a serious answer, I own my on stupid company of stupid techs but I do know how to read a manometer and a temperature gage so you don't know either huh stan
    ummmm

    I read that 3 times and still didn't understand it all.

    Who is stan????

    You got stupid techs. Aint that what I said? No I said bad....my bad


    Ok well get your manometer and tell me the pressures. Then get your temperature GUAGE and tell me the saturation temp.


    you want answers, you need to be a pro. and I mean pro status by that. But by the sounds of it and the looks at your typing abilities, I have a hard time believing you would be able to understand the answers given.
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  7. #7
    Join Date
    Jan 2005
    Location
    Ft. Worth Texas
    Posts
    4

    ok,ok off 0n the wrong foot

    Ive had a really bad day, my typing is not bad for 60 year old man who uses one of these things about once a month, and mostly to read email, Thought you guys would be a little more forgiving. Iraq you could stan a little polish yourself. however , If you could forgive me for interrupting and waisting your time you might be surprised what I can understand when presented in a little less than hostile way . no arguments from me sorry I bothered you stan

  8. #8
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    alright.


    well you need to provide a lot more information before we can even attempt to think about a possible problem.


    you need to first find yourself some techs that properly diagnose systems. Then come here for more information. There is a lot here.
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  9. #9
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,774
    Ok, so then what were the readings.
    OD temp
    ID temp DB and WB
    TESP/ air flow in CFM
    Vapor line temp
    Liquid line temp
    Return air temp DB and WB
    Supply air temp DB and WB
    Did you check both sides of strip heaters for amp draw to make sure they are not on?

    Other then pressures, and that its blowing out hot/warm air, what did you check. What did you try to correct the problem.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    This is starting to belong in technical ..... lol
    ___________________________________________


  11. #11
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,774
    Other then the one question.
    I didn't give any clue how to check anything proper.
    I just asked what the readings were.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    Join Date
    Apr 2008
    Location
    TEXAS
    Posts
    1,701

    Talking

    some times i think every body in texas is scared to call for a/c pros. alot of our calls are fixing what diyers have screwed up or they have a neighbor that used to work on automotive a/c. they always try to cover it up, but the wife will tell you before you can walk in the door that the old skinflint has been monkeying with it. its hilarious.
    "When the people find they can vote themselves money,that will herald the end of the republic" - Benjamin Franklin

    "Government is not reason, it is not eloquence, it is force;like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action"- George Washington

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event