    What makes efficiency?

    The equipment manufacturers all have different lines of equipment that have different efficiencies. The least efficient being 13 SEER and the most efficient being over 20.

    My question is "What changes are made to improve efficiency in a design?"

    I see that the more efficient Trane systems have a much larger condenser, so the size of the coil might be part of the answer.

    What makes an efficient design?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,987
    Post Likes
    Giant outdoor coil. Giant indoor coil. Compressor. 2 stage/ or 2 compressors. Smaller HP condenser fan motor, or a VS condensre fan motor. Line set size requirement.
    Requirement of a VS blower.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,603
    Post Likes
    What 'beenthere' stated, along with some added opinions.
    Beenthere: "2 stage/ or 2 compressors. Smaller HP condenser fan motor, or a VS condenser fan motor, and a 'Requirement' of a VS air handler blower."

    It appears the design-engineers' idea is to do more with larger coils while using smaller more efficient motors.

    However, it appears that the laws of physics cannot be violated or avoided.
    Back in the mid-1970's when I got into HVAC Tech work some of the compressors had higher Btu/hr ratings than the Rating of the matched condenser & evaporator coil.

    Under higher load conditions those compressor's would pull a lower pressure & temperature; a much colder evaporator.

    When the higher loads, any combination of latent & sensible heat, boils off the liquid refrigerant in the E-Coil faster than the compressor can handle it, the pressure & temperature rises.

    If my memory is accurate, some 2-ton condenser's has +26,000 & 27,000-BTUH compressors. They could handle a big heatload increase in the rate of evaporation boil off & keep the pressure & temperature within reasonable dehumidification perimeters.

    Of course, that higher pressure increases, to some degree, the volumetric capacity of the smaller capacity compressor, however, the pressure/temperature of the E-Coil could be above the dew-point of the air going through it.

    Well, when you get all the new engineering 'beenthere' mentioned, the new equipment does a fantastic job.

    Add to the above by 'beenthere,' a digital adjustable half degree increments differential up to 3 or 4 degrees from the t-stat setpoint, which would reduce the number of cycles & the SEER Rating will once again improve. EER is another story... - udarrell
    AOP Forum Rules:

    Rules for Posting

    Rules For Equipment Owners

    Equipment Owners Find a Contractor HERE!

    Free online whole house load calculator & Sizing: http://www.loadcalc.net/ Anyone can use it...!