Results 1 to 13 of 15
Thread: Enough Flow ?
    North Ga.
    Enough Flow ?
    Have a single 2.5 ton a/h v/s and a 2 ton compressor.
    The fan speed is set at 350 cfm per ton or 700 cfm total.
    This is a 1 1/2 storey house w/ 1,000 s/f down & 600 s/f up stairs.(Spray Foam Insulation)
    To cool the upstairs, I have to all but close every supply duct damper that feeds the 1st. floor.---> 10 ea. 6" rigid pipe....( as a side note there are 3 ea. 8" return ducts on the 1st floor.)
    Supply ducts feeding the upstairs (dampers wide open) are as follows--->2ea. 8" rigid pipe, approx. 40' in length...and approx. 5 ea. 90 degree fittings on each duct.......also 1ea. 6" rigid pipe going upstairs.
    Upstairs there is 1ea. 10" return main trunk w/ 2ea. 8" pipe splitting off the main pulling air from the 2 bedrooms.
    With dampers positioned as they are, I get a 3 degree differential between up & downstairs
    My question is....With a educated guess (without doing a s/p test)with the 1st floor duct dampers being closed approx. 85 to 90% will this harm the system?
    thanks for any imformative response...
    Best guess is yes,it will harm it over time.
    Have it tested and see about some duct remediation ,for the second floor.
    Lancaster PA
    I'd guess yes also.
    Neither the compressor or the VS motor are going to last long like that.
    North Ga.
    Thanks for the replys !
    Do you think if I opened all 10 of the 1st floor 6" supply dampers to approx 1/4 to 1/3 from fully closed position,
    that I would increase the airflow enough that I would be safe as far as static pressure or any thing else goes
    Lancaster PA
    Guessing at that could cost you a compressor.
    Have the system checked and the ductwork corrected as needed. Compressor change outs aren't cheap.
    Jun 2007
    atlanta, GA
    You can rig it any way you want but the end result will be the same. An expensive motor module repair and(or) more expensive compressor. When all else fails do it right.