    Furnace size VS. Man. J

    After calculating with man. J (on paper) a house shows 70400 (71* HTD). I am looking at goodman 90+ equipment. The 70 would undersize by 4000, the 90 would over by 14. Man. J says stay tight to results. Opinions?

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,234
    Go with the 90.

    Nothing worse then finding out that the gas company is suppling gas with a 100 BTU lower content then you thought when its at design temp outside. That could put you at 10,000 BTUs light.
    Contractor locator map

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,304
    I'd go less. I did that on mine, and it keeps up just fine when it's -25˚ out.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,234
    Quote Originally Posted by mayguy View Post
    I'd go less. I did that on mine, and it keeps up just fine when it's -25˚ out.
    Shows that your calc was inaccurate.

    Not knowing how inaccurate his calc is, and in which direction, undersizing could mean he has a 10° cooler house at design.
    Contractor locator map

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Apr 2008
    Location
    Alberta Canada
    Posts
    2,246

    it is based on output

    If the furnace is 70,000 x 90% = 63000 output and a 90,000 x 90% = 81,000.
    I would go with 90,000 just incase R-valve was high on something. Have a small safety factor.
    Do it right the first time.

  6. #6
    Join Date
    Jul 2005
    Posts
    717
    Quote Originally Posted by 21degrees View Post
    If the furnace is 70,000 x 90% = 63000 output and a 90,000 x 90% = 81,000.
    I would go with 90,000 just incase R-valve was high on something. Have a small safety factor.
    ************************************************** ********
    My thoughts exactly. Go with the larger one and get the benefit of shorter, but efficient, comfortable cycles, like my furnace with only about 2 six minute burner cycles an hour even at design temperature.