Bryant Question?
I have one contractor telling me he can put in a preferred model 165ANA048 with air handler # FV4BNF006. Another one told me today that Bryant does not recommend or allow that match. Is that combination acceptable? Thanks!
-
06-19-2008, 10:58 AM #2
Professional Member*
- Join Date
- May 2007
- Location
- DC Metro area
- Posts
- 3,223
Well, of course it's not a match--that air handler doesn't exist.
The FV4BNB006 would be the correct model number and would be a rated match at 13.0 EER and 15.5 SEER--great match-up ratings. Could be a mistake on one contractor's behalf. The *006 is modular (doesn't have a single-piece cabinet).
-
06-19-2008, 01:51 PM #3
Banned
- Join Date
- Aug 2002
- Location
- Office and warehouse in both Crystal River & New Port Richey ,FL
- Posts
- 18,836
I believe the F instead of the B is for "Florida",extra cabinet insulation required by code.Could be sold in other areas as well.
-
06-19-2008, 02:41 PM #4
Professional Member*
- Join Date
- May 2007
- Location
- DC Metro area
- Posts
- 3,223
I was just going by what I read in the FV4B product data (http://www.xpedio.carrier.com/idc/gr...t/fv4b-4pd.pdf). It says the "B" specifies "modular," which I would assume means a 2-piece cabinet. It could mean more insulation, though--I don't know.