    Carrier ?

    I received a info on a 4 ton 24ACA348 with a 5 ton variable speed handler FV4BNB006000. What SEER does that give me? Is this a good match? It is a 2200 sq ft home under air in S.Fla. Thanks!

  2. #2
    Join Date
    Jun 2008
    Posts
    25
    You need 400 cfm airflow per ton of AC. A lot more may not be so good.

  3. #3
    Join Date
    May 2007
    Location
    DC Metro area
    Posts
    3,223
    Quote Originally Posted by Jersey ED View Post
    You need 400 cfm airflow per ton of AC. A lot more may not be so good.
    That blower is a match for 2.5-5 ton outdoor units. Coil configuration/size/metering varies, as does fan hp for the fan coils. The airflow can be adjusted. 11.7 EER, 14.5 SEER.