  1. #27
    Join Date
    Apr 2007
    Posts
    6,285
    If they are having a hard time locating the leak have them isolate each component and pressure test each one. Lineset, evaporator, condenser. That will tell you right off the bat. Once they know what is leaking they can focus in a little better. If they don't seem to interested find someone else that is.

    I haven't' had very good luck with those linesets that disappear into the ground

  2. #28
    Join Date
    May 2007
    Location
    Naples, Fl
    Posts
    889
    Quote Originally Posted by iraqveteran View Post
    3 stories.......I bet its between story 2 and 3.
    Other than if someone has done remodeling/decorating and caught the line set with a screw or nail the leaks in this part of the county are usually under the slab. And they're usually in the required pvc/poly chase way but nobody bothered to seal them so the linesets sit in water loaded with all kinds of chemicals from landscape maintenance. Getting the charge right is interesting also. This happens way too often,

  3. #29
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,594
    I have no idea what your talking about.

    Sometimes when I do 2 responces in a row, the quote message stays clicked.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #30
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,371
    Quote Originally Posted by jrbenny View Post
    How ya gonna use those bubbles on the coil and line set?
    A (fairly competent in my opinion) tech at my house once sprayed bubbles on the coils (indoor and outdoor) as well as the valve areas, but I see what you're saying; it's gotta be tough finding a leak with those fins unless its on a u-bend at the coil. You can't use the bubbles on the whole lineset obviously, but in areas where brazing was done and the lineset is exposed I don't see why not. I know you know all of this already; I'm just explaining myself.

  5. #31
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by RyanHughes View Post
    Still may not be in the lineset. Lineset leaks are pretty rare since the copper is one piece. They should look at the places where they brazed the copper (i.e. joints, at unit, etc.). They may have messed up the schraeder core/valve while brazing or not tightened it. Have them back to do it right. They can isolate the leak with soap bubbles.

    have you never seen fittings in the middle of a lineset?

    oh ya, you not an hvac guy!

    you need to get a job in the hvac field, i think you would really like it



    .

  6. #32
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,371
    Read the next sentence. "They should look at the places where they brazed the copper (i.e. joints, at unit, etc.)." Obviously, if there were joints in the lineset due to the length, then they would need to look there, though that'd be difficult if it's burried. I shouldn't have assumed that the lineset was one piece given the length; you are correct. Thanks for pointing that out. I knew you were excited to point out a mistake and then throw a comment about me not being in the HVAC field (which is actually not a requirement to post here according to the admin, whom I've communicated with to confirm my posting privileges--just gotta follow the rules like everybody else)... I thank you for pointing that out about joints in the lineset, which slipped my mind.

  7. #33
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,189
    Back to the reason that I don't think homers should comment on these topics.
    Perhaps you should have read the instructions before calling.

  8. #34
    Join Date
    Mar 2003
    Posts
    7,326
    Sometimes you can get a general location of the leak if there appears to be oil present. It should not be there. Feel around the piping where it connects at both units, if you find oil, you will be close to your leaker....

  9. #35
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    Quote Originally Posted by jrbenny View Post
    Back to the reason that I don't think homers should comment on these topics.
    Homers?

  10. #36
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,371
    Quote Originally Posted by gary_g View Post
    Homers?
    I think it's slang for homeowners.

  11. #37
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    Quote Originally Posted by RyanHughes View Post
    I think it's slang for homeowners.
    Then we are all homers.

  12. #38
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,594
    Quote Originally Posted by gary_g View Post
    Then we are all homers.
    Not if you live in a condo.

    Then your condomer. LOL
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #39
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,189
    Not worth it.
    Perhaps you should have read the instructions before calling.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event