    I realize dehumidifers are rated by how many pints of moisture they remove/hr, but how is that determine ? Is it determined by the number of fin's on the condenser or the size of the compressor or something else....

  2. #2
    Join Date
    Sep 2006
    Posts
    1,253
    They are rated based on energy used vs. water removed = Pints/kWh. The link is a listing of Energy Star rated units. Check out how much more Teddy Bear's Therma-stor units extract.

    http://www.energystar.gov/ia/product..._prod_list.pdf

  3. #3
    Join Date
    Dec 2007
    Location
    Cedar Grove, Wi-Sheboygan
    Posts
    1,582
    I understand that but it still doesn't answer my question as to how they come up with how much the dehunidifer will remove. Is it the size of the comressor or the condenser that makes one remove more water then the other ??? How do they get one to remove 30 pints and another to remove 50 pints is what I want to know.

  4. #4
    Join Date
    Jun 2001
    Location
    DFW
    Posts
    684
    The size of the compressor is the primary driver. However, there also has to be enough 'fins' to match the compressor size. So, the size of everything goes up to increase capacity.

  5. #5
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    1,962
    It takes X amount of energy to condense X amount of water at a specific temperature and humidity in the space the dehumidifier is located in.
    The energy/capacity is going to be directly tied to the capacity of the compressor to convert electrical energy into the required temperature on the condensing/evap coil so it's surface will maintain a temperature below dew point.
    So yes, it's dependant on both.

    http://www.aham.org/ht/a/GetDocumentAction/i/8187
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,597
    Its by how cold their coil gets, at what the air flow over the evap coil is, at x ° room air temp.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event