    I have a Trane 13i heat pump that will not run during the day when it is hot outside.
    Blower comes on, but the condenser unit just short cycles and will not run. The condenser and fan click on for 1-4 seconds then click off.
    After the sun goes down, everything works good. It runs continuously and cools great.
    Any ideas?????
    Yep.
    You need your contractor or service guy back out. They goofed.
    Western NC
    yeah....
    why did you get the solar option? I didn't think there was anyone stupid enough to go for that gig!!!
    You don't happen to have an agreement with your electric company, do you? Ya know the one where your AC doesn't work at certain times of the day?
    Oct 2007
    Zona
    I do not have a solar option nor have any time of use agreement.
    Quote Originally Posted by iraqveteran View Post
    yeah....
    Western NC
    ok then.
    All we need to do now is get your imagination out of the way are your home free
    How long have you had this unit. And was it serviced in the last 6 months.
    Oct 2007
    Zona
    manufacturer date is 2001 (i've been in the house 1 year).
    It was serviced in the fall....for low freon/refrigerant.
    It's is working real good nw that the sun is down.
    It is clean.
    Western NC
    Was the leak found and repaired when the system was found to be low on refrigerant charge?
    MN
    or was the dirty filter changed and now it is overcharged
    You can't fix stupid
    Western NC
    Quote Originally Posted by cmajerus View Post
    dirty filters aren't changed anymore......they are flipped over
    Oct 2007
    Zona
    Yes, it was freezing up. They found a leak near the outside unit and refilled it.
    It worked good after words, and it is working good at the moment.
    Oct 2007
    Zona
    No dirty filters, I change it every month.
    Call them back. They made a slight error.