  1. #40
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Quote Originally Posted by big windy View Post
    Funny , I didn't ask for bigger , what would he gain by upsizing me ? I will let you know how this pans out. At least I won't be needing a furnace tonight .Thanks for your help.
    yeah

    definately keep us posted. Get on it first thing tomorrow. Don't let them give you the run around. Its your money.
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  2. #41
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,167
    Why wait till thursday, she can do it this morning when they get there.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #42
    Join Date
    Aug 2007
    Location
    MN
    Posts
    2,677
    Quote Originally Posted by big windy View Post
    Funny , I didn't ask for bigger , what would he gain by upsizing me ? I will let you know how this pans out. At least I won't be needing a furnace tonight .Thanks for your help.
    He doesn't he loses money when he has to change it to a smaller one. He sized by the previous equipment size, and lost.
    You can't fix stupid

  4. #43
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Quote Originally Posted by beenthere View Post
    Why wait till thursday, she can do it this morning when they get there.
    oh yeah.....your right.

    Have them there first thing TODAY.

    Actually, I can see the call to the on-call tech right now. You wanna explain why my 12 hour old system is already FREAKIN OUT????? hahaha that would be entertaining.
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  5. #44
    Join Date
    Dec 2007
    Location
    Cedar Grove, Wi-Sheboygan
    Posts
    1,582
    Why not just heat the uninsulated garage and call it good No more oversize equipment !!!

  6. #45
    Join Date
    Jun 2008
    Location
    Downers Grove Il
    Posts
    14
    How did you know about the garage ? It is insulated , but can't put in returns , against code , negative pressure etc. . Ha Ha !

  7. #46
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,304
    Not knowing the age of the home and other info, I would almost want to bet you could get by with a 80,000 model.

    Ask for a manual J, and if you want, you can down load a home owner's manual-J up above for $50.

    All the stuff you got on there, sure hope they did a two stage t-stat???

  8. #47
    Join Date
    Jun 2008
    Location
    Downers Grove Il
    Posts
    14
    Honeywell Pro TH4000 series.

  9. #48
    Join Date
    May 2000
    Location
    Rochester, NY, USA
    Posts
    14,325
    Man, do you have a problem

    First off, I think we can be safe in concluding your furnace is over size

    second, you say the returns are two--14 x 8 and a 6" ???

    a 120K BTU furnace will move 2000 cfm. On a furnace this big, I would install a MINIMUM of 10 x 24 in a bottom return or two 8 x 24, one on each side of the furnace. I think your return is inadequate.



    NOW.....not all is lost. The TUY120R9V5V can handle a 3½ ton air conditioner. Increase your return air to, two 24 x 8 (24 x 10, if it will fit) and--->

    check your dip switch's, I would set them up this way for 3½ tons of a/c~~~~~

    1st stage heat, DIP SWITCH 7 & 8 to NORMAL
    . sw7---on, sw8---off. with a static pressure of 0.5 this should give you a fan speed of 1370 cfm with a delta T of 49° (for *HI* speed set them to sw7---off and sw8---off)

    2nd stage heat, DIP SWITCH 7 & 8 to NORMAL. sw7---on, sw8---off

    AIR FLOW SETTING FOR COOLING

    DIP SWITCH 1 & 2 & 3 & 4 (set the fan speed to 350 cfm/ton)
    sw1---off, sw2---on, sw3---off, sw4---on ~~~~~ with a static pressure of 0.5, these setting will give you 1220cfm.

    If you set the dip switchs to 400cfm/ton the minimum fan speed you will get is 1400cfm
    LOVE has four letters

    So does BEER, DEER,GUNS AND FISH

  10. #49
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,304
    Quote Originally Posted by big windy View Post
    Honeywell Pro TH4000 series.
    You have a heat pump on this set up?? This stat is for a heat pump, and if you have a heat pump, I'd ask for the Honeywell IAQ to get a MUCH better control of the heat pump, and stage the gas furnace.

    But before you do that, we got to fix this "maybe oversized" furnace.

  11. #50
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,167
    TH4110 is a standard 1 heat one cool sat.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #51
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,304
    Quote Originally Posted by beenthere View Post
    TH4110 is a standard 1 heat one cool sat.
    I saw that after I posted, and there is the TH4210 that is for heat pump.

    We don't know off hand of what model he may have.

    Come to think of it, he may very well have the TH4110 being he said the furnace locks out after 10 min... The board is firing off 2nd stage around that time.

  13. #52
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,167
    Plus, I believe the 4210 can be used on fossil fuel fnaces. Like the 5220 can.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 4 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event