Help me Decide Trane or Amer Standard
I have Trane 80 ER furnaces about 12 years old and they work well. All three of my Trane central air units have leaks and I am told should be replaced.
One person is recommendind Amer Standard Heat pumps Heritage 14 and says my exisiting unit will not get the effeciency from the American Standard 15 Heritage.
Another dealer is recommending the Trane XLI5i which has a SEER rating of about 15,, which, if I believe the first guy really will not deliver the effeciency.
On top of that my research saysd that the Amer Std 15 is quieter and much more efficient.
Do I go with the 14 or 15 American Std or the Trane and if the Trane the 14 or 15
-
06-17-2008, 06:45 PM #2
Trane vs. American Standard.
Might as well be a Chevy vs. GMC question.
THEY ARE THE SAME UNIT.
I'd go with the one thats installed properly.I fully support the military and the War on Terrorism.
If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.
If you do know, then do. But do it right. Otherwise, you may not be doing it long.
-
06-17-2008, 08:19 PM #3
Look at the ratings carefully. Most A-S/Trane units won't deliver the full efficiency without variable speed indoor units. So models called 14 won't go over 13 with standard blower. The Heritage 15 or XL15i will not likely go over 14 with standard blower. Also look at the HSPF and heating output numbers. Usually fairly low with these brands.
-
06-17-2008, 08:51 PM #4
Regular Guest
- Join Date
- May 2008
- Location
- smalltown VA
- Posts
- 15
Currently the Am Std Heritage systems are offering SEER ratings straight out of the box with conventional air handlers. These SEER ratings will be increased with the addition of a variable speed air handler. ie. 13 SEER OD Unit with Variable Speed AHU = 13.9 SEER. When moving to the two speed systems of 16+, the 16 SEER Rating applies to conventional air handler and increases to 16.4 with Variable Speed air handler. Can't say for sure about the Tranes, but would suspect that to also be the case with them, as they are the same manufacturers.
Am Std HSPF's are from 8.80 - 9.20.
What brands are higher?
-
06-17-2008, 11:47 PM #5
Professional Member
- Join Date
- Jun 2008
- Location
- Surrey, BC, Canada
- Posts
- 35
If your furnaces are 3 years old, I would recommend replaceing the furnaces and air conditioners. The new higher efficiency systems need the better air flows. The manufacturers have matching charts for coils, furnaces and air conditioners and should be followed with new systems. As to which one, they're the same. Go with the best contractor.
-
06-17-2008, 11:53 PM #6
-
06-17-2008, 11:55 PM #7
-
06-18-2008, 12:09 AM #8
Professional Member*
- Join Date
- May 2007
- Location
- DC Metro area
- Posts
- 3,223
I don't think so. I wish that was the way it is but it's not. Take for example a 4A6H4048B1000A (4-ton Heritage 14) and match it with a 4TEC3F48B1000A (4-ton TEC blower), and you have 13.00 SEER--that's not 14.00 SEER. Some sizes are match-ups with higher-sized indoor units, and this can raise the efficiency, but only slightly (still not 14 SEER). Nevertheless, you can still get a great product made by American Standard/Trane (or another manufacturer!) but with a slightly lower efficiency rating. .5 or .75 SEER isn't that big of a deal when you put it into perspective with the other advantages of the Heritage 14--scroll compressor, sound blanket, etc... Now, this isn't to say I think matching a 15 SEER unit up with no variable-speed blower is worth it. I wouldn't go higher than 13/14 SEER without a variable-speed blower. My opinion.
-
06-18-2008, 07:17 AM #9
If furnaces are 12 years old why not upgrade to variable drive furnace in the spaces that are most occupied during the day and keep rooms that are NOT occupied with existing furnaces.
I would choose Am-Std 14.0 on existing and go to 16.0 heat pumps on variable drives. Be sure to get R-410A systems and NOT R-22."Everyday above ground, is a good day".
"But everyday that you have made a difference in someones life, may insure you stay above ground a little longer".<aircooled>
-
06-18-2008, 09:37 AM #10
A/S efficencys are all about the evap coil you put in. Usually to get the listed seer on the condenser your putting in a evap a ton in size bigger. Or the giagantic 3 foot evap coil on the 5 ton units. VS units are required on the 16 and 18 seer units.
Global Warming or: None like it hot
No pleasure, no rapture, no exquisite sin greater... than central air. -Dogma
-
06-18-2008, 11:49 AM #11
Regular Guest
- Join Date
- Mar 2008
- Posts
- 4
Trane Xl 16 Is Worth The Extra Money
Last edited by mannyparad; 06-18-2008 at 11:50 AM. Reason: TYPO
-
06-18-2008, 08:36 PM #12
Regular Guest
- Join Date
- May 2008
- Location
- smalltown VA
- Posts
- 15
You are absolutely correct. We were recently told by our sales people that these units were "Out of the box" rated SEER. Upon further investigation today (after your post) I found what you say to be very true. Our sales rep "has some splaining to do"I don't think so. I wish that was the way it is but it's not. Take for example a 4A6H4048B1000A (4-ton Heritage 14) and match it with a 4TEC3F48B1000A (4-ton TEC blower), and you have 13.00 SEER--that's not 14.00 SEER. Some sizes are match-ups with higher-sized indoor units, and this can raise the efficiency, but only slightly (still not 14 SEER). Nevertheless, you can still get a great product made by American Standard/Trane (or another manufacturer!) but with a slightly lower efficiency rating. .5 or .75 SEER isn't that big of a deal when you put it into perspective with the other advantages of the Heritage 14--scroll compressor, sound blanket, etc... Now, this isn't to say I think matching a 15 SEER unit up with no variable-speed blower is worth it. I wouldn't go higher than 13/14 SEER without a variable-speed blower. My opinion.
-
06-19-2008, 09:51 AM #13
Regular Guest
- Join Date
- Jul 2005
- Posts
- 435
The Trane XL series if installed as a full system will provide you with a 10 year parts warranty on everything installed including the thermo, and air cleaner if you go that route. The labor is under a 2 year warranty.
American Standard does not offer this warranty.


Reply With Quote