06-19-2008, 05:19 PM #14
Banned
- Join Date
- Aug 2002
- Location
- Office and warehouse in both Crystal River & New Port Richey ,FL
- Posts
- 18,836
Exactly!
Booster fan ,when ducts can't be corrected due to construction.
Improving ducts in an accessable basement ,could lower the static enough to mean that the ducts in the walls are "now" large enough.
Lowering static close to the indoor unit ,makes more available for the farthest runs.
-
06-19-2008, 05:30 PM #15
Professional Member
- Join Date
- Jan 2007
- Location
- N.E. Ok.
- Posts
- 1,296
-
06-19-2008, 05:38 PM #16
-
06-19-2008, 05:40 PM #17
-
06-19-2008, 08:28 PM #18
Regular Guest
- Join Date
- Aug 2007
- Location
- Atlanta, Ga
- Posts
- 213
How much will the booster fan raise the temp of the air coming out of the supply?
Joe
-
06-19-2008, 10:16 PM #19
How many watts is the motor. 3.413xwatt=btu
-
06-19-2008, 10:32 PM #20
Regular Guest
- Join Date
- May 2008
- Posts
- 31
-
06-20-2008, 07:53 AM #21
Regular Guest
- Join Date
- Aug 2007
- Location
- Atlanta, Ga
- Posts
- 213
Use 241 and 137....that would equal 822BTU and 468 BTU
How does that equate to temp
Thanks
Joe
-
06-20-2008, 07:55 AM #22
Regular Guest
- Join Date
- Aug 2007
- Location
- Atlanta, Ga
- Posts
- 213
"Wouldn't this also be true if the ductwork was sized correctly in the first place? A system only makes a max amount of airflow that is distributed right"
Does the booster fan increase CFM above the system design?
Joe
-
06-20-2008, 09:05 AM #23
temp rise =BTU/(CFM*1.08(at sea leel))
-
06-20-2008, 10:44 AM #24
Once installed, you depend on it?
If the power were off to such a fan, the added restriction of the fan itself would greatly reduce airflow, right? Just trying to learn what is what. It seems to me that power to the fan would be necessary in order to get anything like the original airflow. But as has been shown before, sometimes my impression can be dead wrong<g>.
Thank you -- Pstu



Reply With Quote