Lennox problem
Ran into a Lennox that has me pulling my hair out. 3 Ton package heat
pump. It is approx 10 years old with no more than routine maintenance
needed since installation ,until a couple of weeks ago. Condensing motor
keeps going out on thermal overload. First call, it seemed that it was a
bad defrost board. Replaced that, unit did o.k. for 3 days then, out again.
Voltage is 235VAC. The compressor and indoor blower continue to run after
cond. motor quits. To date I have replaced the board, the time delay,
the 1/3 Hp 1075 (original) motor and cap. and have thoroughly cleaned the
coils (twice). I baby sat it for over 3 hours. Unit will come on run between
20 minutes and almost an hour but when outdoor temp gets above 90 degrees
F. Motor will (Click) and opens on thermal again. This unit belongs to a friend
therefore no money has changed hands at my suggestion until it works.
According to Lennox, the original motor was not a high temperature motor so
what gives with this. After 15 years in the business, I have never run into
this problem in the past. Any suggestions would be greatly appreciated.
Festus
-
yeah
change out everything that says Lennox!!! 
Sounds like a wiring issue. You say you've replaced different components, but are you sure you installed new components that are good??? I've seen plenty of motors bad outta the box. I've also seen plenty of defrost controls bad outta the box. Time to go back to sqare one.
Also, apply for pro. We can't really help you here in open forum. So thats all I will say.
I fully support the military and the War on Terrorism.
If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.
If you do know, then do. But do it right. Otherwise, you may not be doing it long.
-
change out everything that says Lennox!!!
Ah, no luck with Lennox for ya? I've heard their commercial L Series unit is nice at least.
-
Twilli says have Ruthie yank it out
No Heat No Cool You need Action Fast
-
 Originally Posted by RyanHughes
Ah, no luck with Lennox for ya? I've heard their commercial L Series unit is nice at least. 
Luckily, I don't have to see too many Lennox units anymore. And the only ones I see are the newer commercial units. They are ok.
If it weren't for bad luck, I'd have none at all. Have had 2 days off in the last 4 weeks. and spent both days cuttin grass. Go figure.
I fully support the military and the War on Terrorism.
If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.
If you do know, then do. But do it right. Otherwise, you may not be doing it long.
-
I've had severley burnt breaker may cause this problem, if the unit has a hard start, the compressor would still start, if the unit was misswired, the only way it would run that long is if the run wire to the condenser motor is wired to the herm on the comp run cap. You could have the Wrong size run cap or a low run cap. Ive never had a Bad motor from lennox, A burnt defrost contacts in the control would do it, Hmm
-
Thanks for reply to lennox fan problem. As of now I've tried 2 new defrost
boards. They each do the same thing. On a call for cool the indoor blower,
compressor, and condensing motor all start as expected. After a few minutes
I can hear a "click" in the motor area and the cond. motor stops. The rest
continues to run. I've tried 2 new combo caps (a 40/5) 370V and that makes
no difference. The wiring checks ok to the cap. I've even tried just a single
5mfd run cap and the same thing happens. One new motor was an A.O. Smith
the other I tried is a G.E. 1/4 HP 1075 RPM. Both new motors did the same.
Something (excessive heat from coil or compressor is shutting these motors
down on thermal) What gives with this piece of crap???
-
Thanks for reply to lennox fan problem. As of now I've tried 2 new defrost
boards. They each do the same thing. On a call for cool the indoor blower,
compressor, and condensing motor all start as expected. After a few minutes
I can hear a "click" in the motor area and the cond. motor stops. The rest
continues to run. I've tried 2 new combo caps (a 40/5) 370V and that makes
no difference. The wiring checks ok to the cap. I've even tried just a single
5mfd run cap and the same thing happens. One new motor was an A.O. Smith
the other I tried is a G.E. 1/4 HP 1075 RPM. Both new motors did the same.
Something (excessive heat from coil or compressor is shutting these motors
down on thermal) What gives with this piece of crap???
-
I will sign up for pro as soon as I get a few more posts under my belt,
behind my back or over my head. Any help now is appreciated.
-
Is the motor spinning the right direction????????
I fully support the military and the War on Terrorism.
If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.
If you do know, then do. But do it right. Otherwise, you may not be doing it long.
-
-
Why are you putting on 1/4HP motors if the original was 1/3?
Is the fan blade original, or was that replaced.
-
 Originally Posted by cmajerus
they can keep em  Gotta love the split condenser setup, 30 tons units have access doors to backflush the coils but the middle sections you have to crawl up top and remove the fan guards to hose them out. 10,000 relays, and all kinds of extra parts to diagnose. At least there is about 20 of everything to swap around if you get stumped 
don't forget the Lennox trademark. Every wire is the same freakin color. With tiny little numbers at each end. Good luck tracing.
I fully support the military and the War on Terrorism.
If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.
If you do know, then do. But do it right. Otherwise, you may not be doing it long.