    Requesting a litle advice - ac correct r22 charge.
    Recently we had a new York furnace and evaporator coil (with txv) installed to replace aging units. We had it installed when it was still quite cold outside and I have a question regarding the freon R22 charge which was set after the coil was installed. The tech simply checked the charge by adjusting it to suction 65psi. I feel he should have set the charge by using the subcool method. I believe the outside temperature on the installation day was about 60 degrees. Should I insist that they come back to recheck the charge or is their "rule of thumb" method really good enough and to be trusted/accepted? The 65 degrees suction pressure is approx. 38 degrees at the evap coil, but is the system going to perform as it should?
    Thanks for your input!
    Grundy Co. IL
    I didn't know there was a rule of thumb, you might want to invite him back over.
    They just guessed based on whatever.
    It should be checked by SC, SH, and temp drop across the coil.
    leland nc
    call them and get it checked
    that is not how to ajust anything and you may even be over charged
    Grundy Co. IL
    Does rule of thumb mean, if you put your thumb on the big line and it's cold, you're O.K.?
    Western NC
    Quote Originally Posted by Jay 41 View Post
    no.
    rule of thumb is two fold. You use your left thumb to check return air and right thumb to check supply air. Once done, return left thumb to arse and return right thumb to mouth. Be sure you do the L test before returning thumbs!!
    rule of beer states beer can cold is proper operatin levels for the cold stuff
    rule of wave states wave your hand in front of register. If you feel air coming out, you have proper CFM.
    And the final rule.......
    If the customer is happy, I'm haulin arse before they change their mind!!!!
    Grundy Co. IL
    Quote Originally Posted by iraqveteran View Post
    no.
    Nice, very nice, thanks for the in depth answer.lol
    Ohio
    Here's the formula he was using....
    Outdoor Ambient
    (minus)
    Indoor Wetbulb
    (plus)
    Physical weight of unit
    (plus)
    Ounces in a 12 pack
    (minus)
    Technician's I.Q.
    Equals 65
    Just call him back and make him do it right.
    I need a new signature.....
    Grundy Co. IL
    Quote Originally Posted by I_bend_metal View Post
    Outdoor Ambient
    (minus)
    Indoor Wetbulb
    (plus)
    (plus)
    Ounces in a 12 pack
    (minus)
    Technician's I.Q.
    Equals 65
    Holy s***, these formulas get better every time, anybody else got one.
    Western NC
    Sure
    Outdoor Ambient Temp (DB) + Amount of service calls to run + Mileage to customers house + Diagnostic + Cost of gas + High Side PSIG (after gassing unit) = new hourly rate.
    multiply new hourly rate times amount of time invested in customer(including travel time to and from BFE) and you get new subtotal.
    Take our usual 85% off the top and hand to the rest into the boss. Don't forget to water the bushes at no extra cost.
    Oct 2006
    Only By Subcooling If Is Txv Sys At Least 60 F Ambiant!!!!!
    Jun 2005
    SW Wisconsin
    Quote: "By Subcooling, if it is TXV Sys At Least 60 F Ambient." (True, & more)
    First, charge is only done & accurate, if airflow is within specifications.
    Superheat should also be checked to see if it is holding near its setpoint.
    If there is also very low indoor load on the coil the Subcooling will not be accurate & the Superheat will not hold its setpoint.
    A standard TXV "loses load adjust-ability" at about 30% of its rating.
    Balanced port TXV's lose load adjust-ability at about 15% of rating.
    Let me know if you have data directly contradicting those statements!
    http://www.udarrell.com/ac-trouble-s...ubcooling.html
    - udarrell