    Ok, if it wasn't going to be finnished. I was going to suggest using it as a dump zone. But that won't work for a finnished basement.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Jun 2008
    Posts
    128
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Ok, if it wasn't going to be finnished. I was going to suggest using it as a dump zone. But that won't work for a finnished basement.
    My understanding of the plan is to use a bypass damper back to the return duct and the zone controller will slow down the blower when only 1 zone is calling.

  3. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,889
    Post Likes
    Even in first stage, you can only slow the blower so much before the coil will freeze, or the zone systems anti freeze protection shuts the A/C off.

    You system in first stage is roughly 80% of full capacity. So a overly small zone will require a large amount of bypass air, cooling the coil more yet.

    If you have a zone that is only say, 12,000 BTUs at design temps(or 25% of system total capacity). thats about 800CFM of bypass in first stage.

    There are zoning systems that are designed with that in mind, and also help to prevent short cycling from one zone calling 5 minutes after another zone is satisfied.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #17
    Join Date
    Jun 2008
    Posts
    128
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Even in first stage, you can only slow the blower so much before the coil will freeze, or the zone systems anti freeze protection shuts the A/C off.

    You system in first stage is roughly 80% of full capacity. So a overly small zone will require a large amount of bypass air, cooling the coil more yet.

    If you have a zone that is only say, 12,000 BTUs at design temps(or 25% of system total capacity). thats about 800CFM of bypass in first stage.

    There are zoning systems that are designed with that in mind, and also help to prevent short cycling from one zone calling 5 minutes after another zone is satisfied.
    I'm pretty sure they are using the Nordyne panel with a supply temp sensor and some sort of "modudamper" that controls the bypass based on the blower speed and zones calling.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.