    5/16 liquid Vs 3/8

    Old condo had a 30 yr old Trane 1.5 ton HP

    5 /16 and 5/8 lineset , cant measure length but id guess atleast 80 feet long , 2nd story

    Im installing a Thermal Zone 1.5 410

    This gonna work ?

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Rheem products are OK with smaller liquid lines but that's a long ways. At a glance probably be OK.

    http://www.thermalzone.com/Heat%20Pu...SEER-Specs.pdf

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    I’d call the factory and get approval. Hate to have a problem down the road

  4. #4
    Join Date
    Mar 2015
    Location
    ARK.
    Posts
    3,389
    Post Likes
    Agree.
    It will "work" on a 1.5 but don't expect the eff rating your after.

  5. #5
    Join Date
    Jan 2015
    Posts
    53
    Post Likes
    We used to reuse the Lennox RFC lines on occasion Lennox support said it would work if coil volume was similar
    or smaller, and it did, but I'm sure mrkelly is right.

  6. #6
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Well its runnin , dont know how well yet, friggin sky opened up right as i fired it up , told them i will be back tomoro and i left.

  7. #7
    Join Date
    Mar 2015
    Location
    ARK.
    Posts
    3,389
    Post Likes
    We used to reuse the Lennox RFC lines on occasion
    Not to go off topic.
    You could actually use an RFC liquid line.However,the "trick" back then was to remove the small cap tube or restrictor from inside the condensing unit it worked with and rig it in front of the RFC line and remove the expansion "device" from the new ecoil.The actual "line" itself was never correct to "function" as a metering device as many thought,Still,a bad idea to use them.

  8. #8
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    Be sure to open up the end of the line after you use your tubing cutter. I have had the same situation. Got a call on an American standard Heritage 14 with a small liquid line like that. It was a 3 ton heat pump. Seemed to work fine. Subcooling and superheat was right on. Coil delta T was right on.

  9. #9
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Exactly my thougts as i cut the line, reamed the end out.... yup

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    The 5/16" tubing should work OK if you have enough subcooling at the unit to account for the line pressure drop plus the loss from static lift to the second floor. Here I used the Tecumseh line size app, assumed 100 ft equivalent length and 20 ft lift.

    Name:  1.5 ton R410A .3125 od tube.png
Views: 1932
Size:  39.4 KB

  11. #11
    Join Date
    Mar 2015
    Location
    ARK.
    Posts
    3,389
    Post Likes
    Basically,you will have to stack the cond in order to get flow so little higher head psig will be "acceptable" in the real world.

  12. #12
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    412
    Post Likes
    i have several apartments that are 1.5 ton r-22 units that have 1/4 liquid lines and are 3 story lift with about 225feet LL they run fine. the apartment owner doesn't want to go 410a so idk how they would run like that. replacement of those linesets is 100% out of the question.

  13. #13
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Did you say 225 feet of lineset ? Holy friggin cow

  14. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Birmingham View Post
    i have several apartments that are 1.5 ton r-22 units that have 1/4 liquid lines and are 3 story lift with about 225feet LL they run fine. the apartment owner doesn't want to go 410a so idk how they would run like that. replacement of those linesets is 100% out of the question.
    R410A will work better then the R22 units do. R410A requires less volume then R22.

  15. #15
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    My 1 chart shows a max LL of 240'(TEL). using 5/16.

  16. #16
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    412
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    Did you say 225 feet of lineset ? Holy friggin cow
    ITs stuipid, they ran all the line sets in 4 inch pvc under the slab from one end of the apartment complex to the other, its 5 units long and 3 stories high, so its probably at least 200 feet. the head pressure difference between the units with far line sets and the close ones is about 75psi. in the same conditions.

  17. #17
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    75 psi diff between units? There's something else at play here. IF the only diff between unit is the LL length, 75psi is out of line.

  18. #18
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    75 psi diff between units? There's something else at play here. IF the only diff between unit is the LL length, 75psi is out of line.
    Go to the line sizing app to see what happening:

    Name:  225 ft run 3 story lift.png
Views: 1070
Size:  36.9 KB

    I'll bet dollars to donuts those units with higher discharge pressure also have a lot more subcooling as well. The liquid line pressure drop and equivalent temperature loss will tell you that.

  19. #19
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Tks ice, i was looking at 5/16 not 1/4. Now my chart shows only 100' for 1/4 w/18,000btu.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •