compressor internal locked
is there any suggestion how to get a 4 ton hermetic copeland unlocked beside to replace it !!
its pop the 40 A breaker instantly.
thank for any input.
-
06-15-2008, 01:03 AM #2
Regular Guest
- Join Date
- Oct 2006
- Posts
- 28
did you check if is windings are gorunded??? also owm out winding.....and try to add hard star kit..........my ex boss (plumber) told one time to hit the compresor with 2x4 and hamer on top of of compresor.....i ruther to hit him on the head with 2x10 and slage hamer.....
)
-
06-15-2008, 01:46 AM #3
Professional Member
- Join Date
- Jun 2008
- Location
- Surrey, BC, Canada
- Posts
- 35
A hard start kit may work. I would recommend that you replace the entire system rather than the compressor. Replacement compressors generally have half the life as the original compressor. Is replacing the compressor really in the clients best interest?
-
06-15-2008, 02:04 AM #4
hehehehe............PoP goes the weasel............

heh...If'n ya reset the breaker and turn the system on and the breaker goes.................whack...
I think.
yah may need a new one..........
I couldn't resist...............
-
06-15-2008, 03:16 AM #5
If it trips the breaker instantly, a hard start ain't gonna help it now.
-
06-15-2008, 07:38 AM #6
Professional Member
- Join Date
- Apr 2008
- Posts
- 31
If your breaker is tripping as soon as you reset it the compressor is more then likely grounded. If it was locked up it would not trip the breaker right away. To make sure that it is a grounded compressor you can ohm out the terminals on the compressor.
-
06-15-2008, 08:17 AM #7
-
06-15-2008, 11:40 AM #8
Regular Guest
- Join Date
- Jun 2007
- Posts
- 18
compressor internal locked
i did check the winding , there is no grounded , and hard start kit dont help neither. disconnected the crankcase heater,it was open anyway .
knocked with 2x4 many time, it just dead , trip the breaker immediately .
winding read resistant 5 x 4 x 1.
its rheem unit 14 years old.
replace the comp only is the best choice for the money today.
not much different but it still get the full comp warranty.
thanks everyone
-
06-15-2008, 12:31 PM #9
could try a bigger breaker if you like but most likely it will trip also
time to replace
14 years isnt worth a new compressor imho
-
06-16-2008, 11:34 PM #10
Professional Member
- Join Date
- Apr 2004
- Posts
- 106
-
06-15-2008, 12:57 PM #11
You should of used the old analog "needle meter" because it is shorted through the oil. I love the digi's, but not for checking that.
And, if you just replace the compressor at least replace it with a scroll. Step ur game up a notch.
Replacing the condenser would be an improvment for both you and the customer in most cases.
-
06-15-2008, 01:16 PM #12
Hook it straight to the main, Have the electric company on speed dial and the fire department on the other cell phone's speed dial.
seriously. It sounds like its time to replace at least the compresssor
-
06-19-2008, 09:51 PM #13
Regular Guest
- Join Date
- Oct 2007
- Posts
- 5
Time to replace!!!!!!!