    Quote Originally Posted by twilli3967 View Post
    Twilli says they shouldn't go thru brick wothout protection
    Jay says morter and copper are good friends.

  2. #93
    Join Date
    Jan 2007
    Location
    N.E. Ok.
    Posts
    1,360
    Quote Originally Posted by WorryWart View Post
    So basically, on the install the primary issues I'm hearing are:

    (1) the original copper piping was too small for new unit and instead of installing new piping they crimped the pipe. Should be redone? Will it damage the unit if not fixed?

    (2) Drainpipe issues.

    (3) All the wires in front of the inside unit

    (4) No outisde kill switch

    Anything else that is glaring and necessary on the install end?
    Your heat pump should be elevated, above average snow level for your area.
    I can't believe the trap on the drain line hasn't caused you water issues yet, need to get that corrected fast.

  3. #94
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Quote Originally Posted by captube View Post
    Your heat pump should be elevated, above average snow level for your area.
    I can't believe the trap on the drain line hasn't caused you water issues yet, need to get that corrected fast.
    Okay, I'll add those to the list. I hope he understands when I say "trap on the drainline", cuz I couldn't explain it to him! :-)

  4. #95
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Quote Originally Posted by Jay 41 View Post
    Jay says morter and copper are good friends.
    Alright, I'm pretty sure there is mortar around the copper piping...which could be why they decided to just use what was there.

  5. #96
    Join Date
    Jan 2007
    Location
    N.E. Ok.
    Posts
    1,360
    Quote Originally Posted by WorryWart View Post
    Okay, I'll add those to the list. I hope he understands when I say "trap on the drainline", cuz I couldn't explain it to him! :-)
    If he doesn't understand that

    you are in trouble
    smiley added because i hope you don't take this install as industry standards.

  6. #97
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Quote Originally Posted by captube View Post
    If he doesn't understand that

    you are in trouble
    smiley added because i hope you don't take this install as industry standards.
    OH believe me, I don't. Even I looked at the snarl of lines outside and inside (and crimped pipe) and said....there is something wrong!

  7. #98
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,513
    1= condensate trap ( preferably an easy trap with a flaot switch)
    2= all lines ran from infront of the unit so the blower can be serviced
    3= condensated pump power wire is ran through a drain hole in the coil inclosure and should be ran to a plug
    4= power disconnect needs to be installed outside for the condenser
    5= refrigerant lines should be increased to 7/8 3/8 but he probably will say they are fine

    the duct issues you may have as beenthere said you may have to learn to deal with. Static tests should be done but chances are he wont

  8. #99
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Quote Originally Posted by tinknocker service tech View Post
    1= condensate trap ( preferably an easy trap with a flaot switch)
    2= all lines ran from infront of the unit so the blower can be serviced
    3= condensated pump power wire is ran through a drain hole in the coil inclosure and should be ran to a plug
    4= power disconnect needs to be installed outside for the condenser
    5= refrigerant lines should be increased to 7/8 3/8 but he probably will say they are fine

    the duct issues you may have as beenthere said you may have to learn to deal with. Static tests should be done but chances are he wont
    He may say the refrigerant lines are fine....but are they really?

  9. #100
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    15,843
    Quote Originally Posted by WorryWart View Post
    Would another company be willing to come out and mop up?

    Yes call this company they will clean up that mess.

    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  10. #101
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Quote Originally Posted by Mr Bill View Post
    Yes call this company they will clean up that mess.

    Hey, wait! I think that's the guy that put it in in the first place! :-)

  11. #102
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,901
    Twilli not a hackitte
    No Heat No Cool You need Action Fast

  12. #103
    Join Date
    Mar 2008
    Location
    Grundy Co. IL
    Posts
    773
    Quote Originally Posted by Mr Bill View Post
    Yes call this company they will clean up that mess.

    Where's the pink jug?

  13. #104
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,901
    Twilli had a woman from Tennessee once, she had a nice tooth
    No Heat No Cool You need Action Fast

Page 8 of 24 FirstFirst 12345678910111213141518 ... LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event