    Quote Originally Posted by meoberry View Post
    I had a similar problem if the unit has a GE ECM motor it could be bad bearing in motor. If it is an ecm motor you can fine tune the airflow without no problems but he will have to adjust charge.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  2. #122
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by Mr Bill View Post
    Look we know you spent you hard earned money to get this done and we are not making light of that, most of us here are just working folks so we do understand, so please don't take our sort of humor to serious, we sincerely feel sorry for you that this has happened and the person that installed this should come back and correct some of this mess.
    Peace
    Mr. Bill
    Awww, thanks Mr. Bill. I know it's all in good fun and I quit crying over it about an hour ago.

    Of course, I'll start crying again when I wake up in the morning and the guy comes out and says he doesn't see a problem with the install! Ack!

  3. #123
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by meoberry View Post
    I had a similar problem if the unit has a GE ECM motor it could be bad bearing in motor. If it is an ecm motor you can fine tune the airflow without no problems but he will have to adjust charge.
    Don't know the difference. Does anyone know what kind of motor my unit has and if this would apply?

  4. #124
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    Quote Originally Posted by twilli3967 View Post
    Twiili says call a lawyer and sue, Twilli used to be lawyer

    twilli i heard you sued yourself and defended your self and still lost wth

  5. #125
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Back to the problem raised in the OP..."droning" noise. I've heard certain air handler blower wheels magnify the running bearing noise of the motor attached to the wheel. Nothing wrong with the motor, either. The metal "drum" that attaches the blower wheel cage to the motor hub can act as a resonance chamber, causing a "revolving droning" sound, especially noticeable if the house has metal ductwork. My father-in-law's AR61 Goodman air handler does this. When he bought the house it had all metal ducts in it. The noise about drove us mad. I replaced sections of metal with flex to attenuate the noise. It's now MUCH better. You can still hear the "revolving drone" by the air handler, but not throughout the house.

  6. #126
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by shophound View Post
    Back to the problem raised in the OP..."droning" noise. I've heard certain air handler blower wheels magnify the running bearing noise of the motor attached to the wheel. Nothing wrong with the motor, either. The metal "drum" that attaches the blower wheel cage to the motor hub can act as a resonance chamber, causing a "revolving droning" sound, especially noticeable if the house has metal ductwork. My father-in-law's AR61 Goodman air handler does this. When he bought the house it had all metal ducts in it. The noise about drove us mad. I replaced sections of metal with flex to attenuate the noise. It's now MUCH better. You can still hear the "revolving drone" by the air handler, but not throughout the house.
    Hmmmmm...that's interesting. Is there anyway to insulate the ductwork to produce the same result? I would be concerned about (a) cost and (b) durability of the flex.

  7. #127
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    Look it's easy to find out if it's air flow related or freon pumping through the lines. Heres what you do go outside and "hopefully" you have a disconnect on your outside condenser well flip that sucker off, if no disconnect well kill the breaker to the outside unit and then go back in and turn on the unit inside to the fan on position on the thermostat and see if you still hear the noise.
    As I stated earlier doing this would rule out one or the other.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  8. #128
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by Mr Bill View Post
    As I stated earlier doing this would rule out one or the other.
    Yup, you did! And I didn't! (check it out). I was too afraid to foul around with the switches. Will have to ask my husband to do it when daylight breaks. Sorry for not following through on that immediately...it would certainly have eliminated one possibility.

  9. #129
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    worry you do have good equipment and mrbill is right we do care
    it also realy pisses some of us off bigtime wen someone does work like that

    makes us all look bad imo

    tat issues you have are mostly minor with the exception of the wire for the condensate pump that is a real biggy imo


    say minor doesnt mean i am down playing any of them it means the unit will run but down the road these issues will cause problems you shouldnt be having.

    the guy if he is ligit will step up and fix the issues

    the instalation book that came with both pieces of equipment will explain in detail and also give ilastations of every thing we are saying

    it also will give you the size you need for the refrigerant lines

    he can not argue with that

  10. #130
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by tinknocker service tech View Post
    worry you do have good equipment and mrbill is right we do care
    it also realy pisses some of us off bigtime wen someone does work like that

    makes us all look bad imo

    tat issues you have are mostly minor with the exception of the wire for the condensate pump that is a real biggy imo


    say minor doesnt mean i am down playing any of them it means the unit will run but down the road these issues will cause problems you shouldnt be having.

    the guy if he is ligit will step up and fix the issues

    the instalation book that came with both pieces of equipment will explain in detail and also give ilastations of every thing we are saying

    it also will give you the size you need for the refrigerant lines

    he can not argue with that
    Okay, big surprise....

    I just went down to see if the books were in the pouch on the unit....but it is empty! No manuals!

    Oh my goodness, I am so in trouble.

  11. #131
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Tinknocker,

    Dumb question #492: Where is the condensate pump? Is that the pump on the floor in front of the blower? They didn't replace that--was here when the A.C was. Maybe again they didn't feel like doing the extra work to rewire?

  12. #132
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by WorryWart View Post
    Hmmmmm...that's interesting. Is there anyway to insulate the ductwork to produce the same result? I would be concerned about (a) cost and (b) durability of the flex.
    Is all of your ductwork of sheet metal construction now?

    Flex duct must be sized properly and installed tightly. You would also not need to replace all of the metal ductwork, only the last six feet or so to each supply vent in each room. That's what I did at my FIL's house, for the most part, except the one section of trunk I replaced with a length of flex, as it was easier than doing each supply vent. It worked just fine.

    Here was the full situation that made my FIL's house unbearable until the modifications were made:

    • The construction of the air handler has the blower wheel and motor above the indoor coil.
    • The plenum above the air handler going into the attic is insulated on the outside, not the inside. There is no insulation on the inside to attenuate noise. With this type of duct design (radial), exterior insulation on the plenum is normal and expected.
    • All of the ducts feeding out from the centralized supply plenum were round metal duct, externally insulated. Nothing to dampen both blower and duct noise.
    • Supply grills were stamped steel variety, which are restrictive and can create a "rushing" sound when too much air is forced through the vanes.
    • The nature of the blower wheel described in my last post was transmitted throughout the entire house, along with noise of air traveling through the ducts.
    • "Crosstalk" was also a problem, where people talking in the front part of the house could be heard through the supply vents by people in the back part of the house.
    After my modifications, all of the above problems disappeared, except for localized mechanical noise at the air handler. Being that it's in a hallway, it is not objectionable.

  13. #133
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by shophound View Post
    Is all of your ductwork of sheet metal construction now?

    Flex duct must be sized properly and installed tightly. You would also not need to replace all of the metal ductwork, only the last six feet or so to each supply vent in each room. That's what I did at my FIL's house, for the most part, except the one section of trunk I replaced with a length of flex, as it was easier than doing each supply vent. It worked just fine.

    Here was the full situation that made my FIL's house unbearable until the modifications were made:

    • The construction of the air handler has the blower wheel and motor above the indoor coil.
    • The plenum above the air handler going into the attic is insulated on the outside, not the inside. There is no insulation on the inside to attenuate noise. With this type of duct design (radial), exterior insulation on the plenum is normal and expected.
    • All of the ducts feeding out from the centralized supply plenum were round metal duct, externally insulated. Nothing to dampen both blower and duct noise.
    • Supply grills were stamped steel variety, which are restrictive and can create a "rushing" sound when too much air is forced through the vanes.
    • The nature of the blower wheel described in my last post was transmitted throughout the entire house, along with noise of air traveling through the ducts.
    • "Crosstalk" was also a problem, where people talking in the front part of the house could be heard through the supply vents by people in the back part of the house.
    After my modifications, all of the above problems disappeared, except for localized mechanical noise at the air handler. Being that it's in a hallway, it is not objectionable.
    Thanks for the ideas!

    Frankly, I don't know if all our ducting is metal....they are all pretty insulated if memory serves me, and do metal ducts come in round? I certainly hope that replacing ductwork will not be necessary....although the discussion on this thread leads me to believe it is certainly a possibility. I just don't know why the problem didn't arise with the previous unit!

    I'll keep your checklist handy, in case the other fixes aren't effective.

  14. #134
    Join Date
    Jan 2007
    Location
    N.E. Ok.
    Posts
    1,483
    Post Likes

    never mind i'm going to bed.
    Last edited by captube; 06-13-2008 at 10:56 PM.

  15. #135
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    shophound...

    Yeah, I see what you also had round, externally insulated radial ducts....Sounds like what we have... :-(

  16. #136
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by captube View Post
    Originally Posted by Mr Bill View Post
    Look it's easy to find out if it's air flow related or freon pumping through the lines. Heres what you do go outside and "hopefully" you have a disconnect on your outside condenser well flip that sucker off, if no disconnect well kill the breaker to the outside unit and then go back in and turn on the unit inside to the fan on position on the thermostat and see if you still hear the noise.
    a
    Yup, I will do this in the morning. So if it's not the refrigerant line, then I'll know it can be fixed by either adjusting blower speed or fixing duct problems. Am I finally getting it--please say I am! :-)

  17. #137
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by WorryWart View Post
    shophound...

    Yeah, I see what you also had round, externally insulated radial ducts....Sounds like what we have... :-(
    The previous homeowners at my FIL's place had replaced the original Lennox equipment prior to FIL purchasing the house. No idea what the original tonnage was, but I have a feeling the replacement equipment was upsized. I ran load calcs on that house as it sat before I made mods and the equipment on the ground was oversized according to the load calc. Oversized equipment often means it moves more air than the original equipment. With all metal ducts, that extra air motion will manifest as unbearable noise.

  18. #138
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by shophound View Post
    The previous homeowners at my FIL's place had replaced the original Lennox equipment prior to FIL purchasing the house. No idea what the original tonnage was, but I have a feeling the replacement equipment was upsized. I ran load calcs on that house as it sat before I made mods and the equipment on the ground was oversized according to the load calc. Oversized equipment often means it moves more air than the original equipment. With all metal ducts, that extra air motion will manifest as unbearable noise.
    Yeah, sounds like our dilemma. We upsized to a 3.5 heat pump (from a 3 ton A.C) and the only addition in finished area was 790 sq ft in basement.

    We have an airflow problem into my son's bedroom, and there is only one vent in the basement. I wonder if adding a duct in each place would alleviate the pressure on existing vents? (I have NO hvac knowledge/experience, so please don't flame me on this one!)

  19. #139
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by captube View Post

    never mind i'm going to bed.
    I really appreciate your input and help! Have a good weekend.

    I'll post an update (hopefully a happy one) at some point.

  20. #140
    Join Date
    Jun 2008
    Location
    TN
    Posts
    139
    Post Likes
    Thread Starter

    Signing Off

    Thanks to all of you for being supportive, helpful and interested during my trauma. I'll keep you updated!

Page 7 of 16 FirstFirst 1234567891011121314 ... LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •