Help! I am in serious trouble!
First, I am duly ashamed that I am in this position, and should have done my homework more carefully. Mea culpa and please don't scold me harshly.
My husband and I just junked our 35 year old A/C unit because of a chronic leak in the coolant system (and, frankly, its age). We decided to go with a heat pump, because we live in East Tennessee and that is what you do around here. We are on a limited budget (aren't we all) with a young child. I asked for a recommendation from our neighbor and went with the professional recommended. He seemed nice enough, and his team installed a Goodman 13-SEER GSH130421A/ARUF364216 unit.
The very night of the install I started going crazy because of the excessive noise inside our house (1972 sq foot rancher, 711 finished downstairs, indoor unit downstairs in garage basement). There is a huge rushing sound from both the intake and vents, which I assume is caused by the increased capacity of our new system. I guess I could live with that, although it would be nice if it could cool without hissing at us.
But here is my major issue: There is a major droning noise from the indoor unit that I hear in 4 rooms and the hallway upstairs. I don't really know how to describe it otherwise, since it's not a rattle and I can't discern any scraping. Is there anything that can be done to lessen this noise? It sounds like a factory in here, and I declare I will probably kill myself if I have to listen to this day in and day out. It's a home, for goodness sake!
Have I just messed myself over, or can you help? I called the installer and he said something about coming out and cutting down the speed of the blower, but will that address the drone as well? What should I ask him about and what should he do? What should he have done?
I tried to do my best and live within our budget and am very discouraged. :-( Please help me.
-
06-13-2008, 07:28 PM #2
Wart....when you first had this quote prepared for you did your salesman do a load calculation on your house to properly size your new equipment???
What is the square footage of your home?I need a new signature.....
-
06-13-2008, 07:34 PM #3
Regular Guest
- Join Date
- Jun 2008
- Location
- TN
- Posts
- 133
Honestly, I don't know if he did or didn't. The old A/C was a 3 ton and he said I needed a 3.5 ton.
The upstairs is 1972 sq feet and downstairs was finished recently for an additional 711 sq feet or so. There was a vent in the basement but not a return, so he added a 12x12 there.
-
06-13-2008, 07:34 PM #4
Did they also check to see if the ductwork was sized properly also, if they change blower speeds, this can create other problems as well.
-
06-13-2008, 07:36 PM #5
Regular Guest
- Join Date
- Jun 2008
- Location
- TN
- Posts
- 133
Make that 790 finished downstairs.
-
06-13-2008, 07:37 PM #6
Twilli says another hummer
No Heat No Cool You need Action Fast
-
06-13-2008, 07:37 PM #7
Regular Guest
- Join Date
- Jun 2008
- Location
- TN
- Posts
- 133
-
06-13-2008, 07:38 PM #8
Regular Guest
- Join Date
- Jun 2008
- Location
- TN
- Posts
- 133
-
06-13-2008, 07:41 PM #9
Anytime your air flow is adjusted....they will need to adjust the refrigerant charge in the AC/HP as well. Before they do anything though they need to verify you have the proper airflow for your system by using the blower chart and checking static pressure.
At 3.5 tons outside, your air handler should be moving somewhere around 1400 CFM's of air. Once they verify that, they will need to check the superheat and subcooling on the outdoor unit to make sure the refrigerant charge is correct.I need a new signature.....
-
06-13-2008, 07:43 PM #10
-
06-13-2008, 07:44 PM #11
Regular Guest
- Join Date
- Jun 2008
- Location
- TN
- Posts
- 133
Thank you so much for taking the time to talk me through this.
Will this sort of adjustment affect the efficiency OR effectiveness of the system (either in heating or cooling mode)?
Also, do you suspect that would help with hearing the "engine" sound (for lack of the right term)?
OR do you suspect the system is oversized for hte house?
OR, is it the brand?
-
06-13-2008, 07:46 PM #12
-
06-13-2008, 07:47 PM #13
Mr. Bill says drone noise much better than moan noise in home especially if you have children around.
“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.


Reply With Quote